Ideally, on new installations, the trades are all doing their rough-in at
the same time- the flex connector is part of the rough-in, but it is
zip-tied to the pipe (hydro with the heads installed is nice). After
rough-in the grid is installed, so the other trades will likely not have to
mess with the connector.

Chris- there are advantages to flex connectors even if COT is not required-
one is if res exceeds 100 psi and you have to have 12"+ arm-overs for some
reason, flex connectors would save a lot of hangers.

-----Original Message-----
From: ParsleyConsulting [mailto:[email protected]] 
Sent: Friday, May 28, 2010 10:37 AM
To: [email protected]
Subject: Re: Flexible Heads, a Learnable Moment

One of the biggest problems I've seen with flexible drops here in 
California is that they may be installed perfectly within the listing, 
in terms of hydraulic calculations, number of bends, radii, and so 
forth.  Then, the other trades are making changes to them, inducing 
tighter radii, or more bends than are allowed, with the thinking being 
that "it's flexible, like flex-duct, no problem to move it out of our 
way."  That very situation is what resulted in several municipalities 
here denying their use outright, and several others allowing them on a 
"case by case" basis. 

The other issue where it comes into play here, and I suppose any where 
else in the country where seismic issues take a seat in the front row is 
the ASCE7 requirement for oversize escutcheons for sprinklers in drop 
ceilings which have not been rigidly braced.  The escutcheons are out 
there, but they're decidedly ugly, and the architects go absolutely ape 
when they see them.  Flexible drop fittings are considered an equivalent 
to the oversize escutcheons, which is why I've seen more and more of 
them on designs coming across my desk. 
As an aside, there is some confusion on the part of AHJ's out there on 
this issue, with many of them believing the "rigidly braced" language in 
ASCE7 is talking about fire sprinkler system branch lines, rather than 
the ceilings themselves.  Ron Greenman sent me some information a while 
back from (natch) the ceiling manufacturing group that suggested it is 
indeed applicable to the ceilings rather than the pipe, but I've not 
been able to get any confirmation from the people at ASCE on that.  
You'd think that as the paragraph is in a section on "ceilings" that it 
would be natural, but I guess not.

Have a great weekend, everyone.
-- 
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[email protected] <mailto:[email protected]> e-mail
www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website

Chris Cahill wrote:
> We haven't really found a use for them. 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________