I am having to go through some calculations on hangers to see if a particular truss can handle the sprinkler pipe. The problem is involving Sammys and since they are not specifically listed in NFPA 13 (2002), we need to do the calculations. My question has to do with the swivel rings.
Section 9.1.1.2 requires the 5x wt of water filled pipe + 250 lbs. According to the PHD Manufacturing literature I have, a 2" swivel ring has a design load is 300 lbs. If we deduct the 250, you have 50 lbs left. Divide that by 5 and you get 10 lbs as the maximum weight that can be supported. Since 2" water filled pipe weighs 5.17 lb/ft., the maximum span a 2" hanger can support and meet the NFPA 13 requirements is 1" - 11". Am I missing something here? Todd G. Williams, PE Fire Protection Design/Consulting Stonington, CT 860.535.2080 www.fpdc.com _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)