Sammys are approved, but not specifically detailed in NFPA 13, which 
is this guy's problem.



At 07:12 PM 6/21/2010, you wrote:
>Why are we even talking about "Non-Listed" hanger parts? He said he was
>using Sammy brand wood fasteners. They are listed!
>See FM guide 1-544 and it gives a whole list of approvals for all kinds of
>"Sammy" brand fasteners.(Specifically GST20 and GST30) They also have a U/L
>listing. If you only want a U/L listing there are even more options from
>Sammy.
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of
>ParsleyConsulting
>Sent: Monday, June 21, 2010 4:00 PM
>To: [email protected]
>Subject: Re: Hanger capacity
>
>Chris,
>
>Yes, the standard does say that, only not quite as eloquently as Ron did.
>
>9.1.1.2 lists the requirements for a non-listed hanger assembly provided
>by a structural engineer.
>
>9.2.1.3.1 lists the requirements for the capacity of the building
>structure to accept the load, which is another matter entirely.  You'll
>note that in 9.2.1.3, there's no 5x multiplier.
>
>--
>PARSLEY CONSULTING
>Ken Wagoner, SET
>760.745.6181 voice
>760.745.0537 fax
>[email protected] <mailto:[email protected]> e-mail
>www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website
>
>
>IMPORTANT NOTICE: This correspondence is not a Formal
>Interpretation issued pursuant to NFPA Regulations. Any opinion
>expressed is the personal opinion of the author and does not necessarily
>represent the official position of the NFPA or its Technical Committees.
>In addition, this correspondence is neither intended, nor should it be
>relied upon, to provide professional consultation or services.
>
>
>
>Chris Cahill wrote:
> > "The code says the building needs to hold up X weight of sprinkler piping,
> > water and fat guy."
> >
> > Does the code say that?  The hanger needs this when not listed.  The point
> > of support only needs to be adequate to support the system from the '02
>ed.
> > I don't believe the building code is that specific. The listing as Rich
>said
> > doesn't have this extra apparently. I also submit as evidence all the
>really
> > light weight structural systems that can barely hold themselves up it
>seems
> > never mind the sprinklers without the extra.
> >
> > Chris Cahill, P.E.
> > Fire Protection Engineer
> > Sentry Fire Protection, Inc.
> >
> > 763-658-4483
> > 763-658-4921 fax
> >
> > Email: [email protected]
> >
> > Mail: P.O. Box 69
> >         Waverly, MN 55390
> >
> > Location: 4439 Hwy 12 SW
> >               Waverly, MN 55390
> >
> > -----Original Message-----
> > From: [email protected]
> > [mailto:[email protected]] On Behalf Of Ron
>Greenman
> > Sent: Monday, June 21, 2010 4:22 PM
> > To: [email protected]
> > Subject: Re: Hanger capacity
> >
> > And of course Todd I'm going to get on my old horse: If you're being
> > the sprinkler guy on this why are you even caring about the load
> > holding abilities of the building? The code says the building needs to
> > hold up X weight of sprinkler piping, water and fat guy. You provide
> > the point loading value to that weight and the owner, through his
> > highly paid and highly skilled reps, architect, GC, structural,
> > whomever is driving that part of the boat makes sure the building is
> > adequate. If you're also being the structural on this then go for it.
> >
> > On Mon, Jun 21, 2010 at 10:59 AM, Richard Mote
> > <[email protected]> wrote:
> >
> >> If you look at the load limit tables from some of the hanger
> >>
> > manufacturers,
> >
> >> you will notice that the numbers do not always equal 5 times the weight +
> >> 250 lbs. This was pointed out to me by a P.E. reviewing a set of plans I
> >>
> > had
> >
> >> submitted. Subsequent conversations between the hanger manufacturer in
> >> question and U/L reveled the following.
> >>
> >> U/L has a set of criteria, hangers and hanger devices have to meet in
> >>
> > order
> >
> >> to be listed. These involve shake tests, pull out, bending moment, twist
> >>
> > off
> >
> >> and a bunch of others. Any hanger that meets U/L's shake and bake tests
> >>
> > gets
> >
> >> listed. Now for the kicker, the listed hanger may not and often does not
> >> meet the 5 X + 250 criteria.
> >>
> >> What NFPA 13 says in its own inimitable round about way is this. Use a
> >> listed hanger assembly, if you don't then engineer it to meet all of the
> >> criteria in 9.1.1.2 (2007).
> >>
> >> One added point, nothing is specifically listed in NFPA 13. NFPA 13 does
> >> give some example illustrations of representative listed product however
> >>
> > it
> >
> >> does not specifically list or indorse any products.
> >>
> >> You can't always go be the illustrations either, for example NFPA 13
> >>
> > (2007)
> >
> >> Figure A.9.1.1, top row third from the left shows a split ring, neat
> >>
> > little
> >
> >> hanger especially for sensing line piping and exposed pipe in atriums and
> >> the like. Problem is last time I went to order them I could not find a
> >> listed split ring from any manufacturer. Now go two spaces to the right,
> >> pipe clamps, try to buy a listed 12" pipe clamp can't be done. I could go
> >>
> > on
> >
> >> but there is real work to be done.
> >>
> >>
> >>
> >> Richard L. Mote ET
> >> Designer
> >> Rowe Sprinkler systems, Inc.
> >>
> >>
> >>
> >>
> >>
> >>
> >>
> >> ----- Original Message -----
> >> From: "Chris Cahill" <[email protected]>
> >> To: <[email protected]>
> >> Sent: Monday, June 21, 2010 12:51 PM
> >> Subject: RE: Hanger capacity
> >>
> >>
> >>
> >>> I have seen recently where the fine print on a load factor already
> >>>
> > included
> >
> >>> the 250 plus 5x.  In my case your 300# would actually be 1750# yielding
> >>> 300#
> >>> useful for our intent.  It wasn't what you are working on, just check
>the
> >>> fine print or talk to the mfg.  Of course at 300#/5#/ft = 60 ft which is
> >>> 4x
> >>> over designed if this is the case.
> >>>
> >>> Chris Cahill, P.E.
> >>> Fire Protection Engineer
> >>> Sentry Fire Protection, Inc.
> >>>
> >>> 763-658-4483
> >>> 763-658-4921 fax
> >>>
> >>> Email: [email protected]
> >>>
> >>> Mail: P.O. Box 69
> >>>        Waverly, MN 55390
> >>>
> >>> Location: 4439 Hwy 12 SW
> >>>              Waverly, MN 55390
> >>> -----Original Message-----
> >>> From: [email protected]
> >>> [mailto:[email protected]] On Behalf Of Todd
> >>> Williams
> >>> Sent: Monday, June 21, 2010 11:40 AM
> >>> To: [email protected]
> >>> Subject: Hanger capacity
> >>>
> >>> I am having to go through some calculations on hangers to see if a
> >>> particular truss can handle the sprinkler pipe. The problem is
> >>> involving Sammys and since they are not specifically listed in NFPA
> >>> 13 (2002), we need to do the calculations.  My question has to do
> >>> with the swivel rings.
> >>>
> >>> Section 9.1.1.2 requires the  5x wt of water filled pipe + 250 lbs.
> >>> According to the PHD Manufacturing literature I have, a 2" swivel
> >>> ring has a design load is 300 lbs. If we deduct the 250, you have 50
> >>> lbs left. Divide that by 5 and you get 10 lbs as the maximum weight
> >>> that can be supported. Since 2" water filled pipe weighs 5.17 lb/ft.,
> >>> the maximum span a 2" hanger can support and meet the NFPA 13
> >>> requirements is 1" - 11".  Am I missing something here?
> >>>
> >>> Todd G. Williams, PE
> >>> Fire Protection Design/Consulting
> >>> Stonington, CT
> >>> 860.535.2080
> >>> www.fpdc.com
> >>>
> >>> _______________________________________________
> >>> Sprinklerforum mailing list
> >>> [email protected]
> >>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>>
> >>> For Technical Assistance, send an email to: [email protected]
> >>>
> >>> To Unsubscribe, send an email
>to:[email protected]
> >>> (Put the word unsubscribe in the subject field)
> >>>
> >>> _______________________________________________
> >>> Sprinklerforum mailing list
> >>> [email protected]
> >>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>>
> >>> For Technical Assistance, send an email to: [email protected]
> >>>
> >>> To Unsubscribe, send an email
>to:[email protected]
> >>> (Put the word unsubscribe in the subject field)
> >>>
> >>>
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> [email protected]
> >> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>
> >> For Technical Assistance, send an email to: [email protected]
> >>
> >> To Unsubscribe, send an email to:[email protected]
> >> (Put the word unsubscribe in the subject field)
> >>
> >>
> >
> >
> >
> >
>
>--
>
>PARSLEY CONSULTING
>
>Ken Wagoner, SET
>
>760.745.6181 voice
>
>760.745.0537 fax
>
>[email protected] <mailto:[email protected]> e-mail
>
>www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to