I have seen recently where the fine print on a load factor already included
the 250 plus 5x.  In my case your 300# would actually be 1750# yielding 300#
useful for our intent.  It wasn't what you are working on, just check the
fine print or talk to the mfg.  Of course at 300#/5#/ft = 60 ft which is 4x
over designed if this is the case.  

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Todd Williams
Sent: Monday, June 21, 2010 11:40 AM
To: [email protected]
Subject: Hanger capacity

I am having to go through some calculations on hangers to see if a 
particular truss can handle the sprinkler pipe. The problem is 
involving Sammys and since they are not specifically listed in NFPA 
13 (2002), we need to do the calculations.  My question has to do 
with the swivel rings.

Section 9.1.1.2 requires the  5x wt of water filled pipe + 250 lbs. 
According to the PHD Manufacturing literature I have, a 2" swivel 
ring has a design load is 300 lbs. If we deduct the 250, you have 50 
lbs left. Divide that by 5 and you get 10 lbs as the maximum weight 
that can be supported. Since 2" water filled pipe weighs 5.17 lb/ft., 
the maximum span a 2" hanger can support and meet the NFPA 13 
requirements is 1" - 11".  Am I missing something here?

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to