We got the local BI to agree to that at the end of the 1st week.........


At 12:45 PM 6/21/2010, you wrote:
>Todd,
>
>What about 9.1.1.4.4?  Doesn't that cover Sammy's since they are listed?
>
>Cliff Whitfield, SET
>President
>Fire Design, Inc.
>
>[email protected]
>www.fire-design.com
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of Todd Williams
>Sent: Monday, June 21, 2010 11:40 AM
>To: [email protected]
>Subject: Hanger capacity
>
>I am having to go through some calculations on hangers to see if a
>particular truss can handle the sprinkler pipe. The problem is
>involving Sammys and since they are not specifically listed in NFPA
>13 (2002), we need to do the calculations.  My question has to do
>with the swivel rings.
>
>Section 9.1.1.2 requires the  5x wt of water filled pipe + 250 lbs.
>According to the PHD Manufacturing literature I have, a 2" swivel
>ring has a design load is 300 lbs. If we deduct the 250, you have 50
>lbs left. Divide that by 5 and you get 10 lbs as the maximum weight
>that can be supported. Since 2" water filled pipe weighs 5.17 lb/ft.,
>the maximum span a 2" hanger can support and meet the NFPA 13
>requirements is 1" - 11".  Am I missing something here?
>
>Todd G. Williams, PE
>Fire Protection Design/Consulting
>Stonington, CT
>860.535.2080
>www.fpdc.com
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to