we put them in wholly different locations on our tanks.
the TLS goes beside the top of the ladder; the TTS goes in the doghouse or
pumphouse on the far side from the immersion heater.
it's another small weldolet on the tank.

glc

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Greg McGahan
Sent: Thursday, July 15, 2010 2:57 PM
To: [email protected]
Subject: Re: water storage tank

They are, and I am too in this particular issue.

The Potter equipment does not comply with the engineers drawings which is
very commonly found and used in other applications. It is a single unit that
mounts on the top and does both jobs (level and temp) at the same time.

I have not been successful in find one that sends the 2 signals regardless
of listing - which is of course a concern as well.

The non listed, single signal units are very inexpensive, but can't use
them. The Potter devices are Listed and send 2 signals, but they don't fit
the rest of the picture.

Thanks,
Greg

On 7/15/2010 10:56 AM, [email protected] wrote:
> Greg,
>   Hopefully they are not clueless about "22". } ; )
>
> LV
>
>
> ---- George Church<[email protected]>  wrote:
>    
>> EZ
>> Potter TTS
>> Potter TLS
>>
>> George Church
>> Rowe Spkr
>>
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of Greg 
>> McGahan
>> Sent: Thursday, July 15, 2010 11:00 AM
>> To: [email protected]
>> Subject: water storage tank
>>
>> Can someone point me in the direction to find switches to meet the 
>> following requirements? The manufacturers I am talking to are 
>> clueless in regards to 72.
>> Thanks,
>> Greg
>> *
>>
>>
>> 5.15.3 Water Level Supervisory Signal-Initiating Device.*
>> *5.15.3.1* Two separate and distinct signals shall be initiated: one 
>> indicating that the required water level has been lowered or raised
>> (off-normal) and the other indicating restoration.
>> *5.15.4 Water Temperature Supervisory Signal-Initiating Device.* A 
>> temperature supervisory device for a water storage container exposed 
>> to freezing conditions shall initiate two separate and distinctive
signals.
>> One signal shall indicate a decrease in water temperature to 4.4°C
>> (40°F) and the other shall indicate its restoration to above 4.4°C
(40°F).
>> --
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email 
>> to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email 
>> to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>      
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]
> (Put the word unsubscribe in the subject field)

--
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to