Todd,
I believe it is linear feet. The "most distant" point for water to travel
(the most time), nothing to do with demand. Size would not matter.

R/
Matt

  

Matthew J. Willis, CET
Automatic Fire Sprinklers
Norred Fire Systems L.L.C.
318-387-1134 Voice
318-816-1087 Mobile
318-387-1163 Facsimile
[email protected]

> >-----Original Message-----
> >From: [email protected] [mailto:sprinklerforum-
> >[email protected]] On Behalf Of Todd Williams
> >Sent: Monday, July 19, 2010 12:59 PM
> >To: [email protected]
> >Subject: dry inspectors test "distance"
> >
> >NFPA 13 (2007) section 8.17.4.3.2: "The trip test connection shall be
> >located on the end of the most distant sprinkler pipe..." How is
> >"distant" calculated? I assume this means it is independent of
> >hydraulic remote areas? Does pipe diameter play into this at all? I
> >am working on an attic system with Tyco Attic BB and AP sprinklers
> >and the physically distant is very different than the hydraulically
> >remote area.
> >
> >
> >
> >Todd G. Williams, PE
> >Fire Protection Design/Consulting
> >Stonington, CT
> >860.535.2080
> >www.fpdc.com
> >
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> >For Technical Assistance, send an email to: [email protected]
> >
> >To Unsubscribe, send an email to:[email protected]
> >(Put the word unsubscribe in the subject field)
> >No virus found in this incoming message.
> >Checked by AVG - www.avg.com
> >Version: 9.0.839 / Virus Database: 271.1.1/3009 - Release Date: 07/19/10
> >01:36:00

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to