This is hard to imagine since it is all one hazard (Light, or you cannot use
attic heads), but the I.T. would go at the highest and farthest.

-----Original Message-----
From: Todd Williams [mailto:[email protected]] 
Sent: Monday, July 19, 2010 12:59 PM
To: [email protected]
Subject: dry inspectors test "distance"

NFPA 13 (2007) section 8.17.4.3.2: "The trip test connection shall be 
located on the end of the most distant sprinkler pipe..." How is 
"distant" calculated? I assume this means it is independent of 
hydraulic remote areas? Does pipe diameter play into this at all? I 
am working on an attic system with Tyco Attic BB and AP sprinklers 
and the physically distant is very different than the hydraulically 
remote area.



Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to