Type IIIA matches up with your area figure. Others have noted the 55 ft criteria although in my version of the 2006 IBC it is contained in the "windowless story" heading but this is now corrected in the 2009 903.2.11. Also note certain areas may require sprinklers because of their hazard (2006 Table 508.2). Watch out for mixed occupancy conditions such as assembly that can trigger a building wide requirement at a lower area threshold. Your basement might require sprinklers. See 2006 903.2.10.
I don't know of a maximum area number, you have to back into it from other directions. Bill Brooks William N. Brooks, P.E. Brooks Fire Protection Engineering Inc. 372 Wilett Drive Severna Park, MD 21146-1904 410-544-3620 410-544-3032 FAX 412-400-6528 Cell -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Todd Williams Sent: Wednesday, July 21, 2010 1:57 PM To: [email protected] Subject: IBC omission? I was looking for the section in IBC where they describe the maximum square footage where sprinklers are not required in a Group B occupancy. I could find reference to all of the other occupancy groups, but not B. Am I missing something? Todd G. Williams, PE Fire Protection Design/Consulting Stonington, CT 860.535.2080 www.fpdc.com _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)