Type IIIA matches up with your area figure.  Others have noted the 55 ft
criteria although in my version of the 2006 IBC it is contained in the
"windowless story" heading but this is now corrected in the 2009 903.2.11.
Also note certain areas may require sprinklers because of their hazard (2006
Table 508.2).  Watch out for mixed occupancy conditions such as assembly
that can trigger a building wide requirement at a lower area threshold.
Your basement might require sprinklers.  See 2006 903.2.10.

I don't know of a maximum area number, you have to back into it from other
directions.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Todd Williams
Sent: Wednesday, July 21, 2010 1:57 PM
To: [email protected]
Subject: IBC omission?

I was looking for the section in IBC where they describe the maximum 
square footage where sprinklers are not required in a Group B 
occupancy. I could find reference to all of the other occupancy 
groups, but not B. Am I missing something?

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to