The building is strictly office (B) occupancy; professional offices. 
Type IIIA or IIIB construction (confirming with owner) around 11000 
sqft stand alone building. No local modifications to IBC.



At 02:41 PM 7/21/2010, you wrote:
>Type IIIA matches up with your area figure.  Others have noted the 55 ft
>criteria although in my version of the 2006 IBC it is contained in the
>"windowless story" heading but this is now corrected in the 2009 903.2.11.
>Also note certain areas may require sprinklers because of their hazard (2006
>Table 508.2).  Watch out for mixed occupancy conditions such as assembly
>that can trigger a building wide requirement at a lower area threshold.
>Your basement might require sprinklers.  See 2006 903.2.10.
>
>I don't know of a maximum area number, you have to back into it from other
>directions.
>
>Bill Brooks
>
>William N. Brooks, P.E.
>Brooks Fire Protection Engineering Inc.
>372 Wilett Drive
>Severna Park, MD 21146-1904
>410-544-3620
>410-544-3032 FAX
>412-400-6528 Cell
>
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of Todd Williams
>Sent: Wednesday, July 21, 2010 1:57 PM
>To: [email protected]
>Subject: IBC omission?
>
>I was looking for the section in IBC where they describe the maximum
>square footage where sprinklers are not required in a Group B
>occupancy. I could find reference to all of the other occupancy
>groups, but not B. Am I missing something?
>
>Todd G. Williams, PE
>Fire Protection Design/Consulting
>Stonington, CT
>860.535.2080
>www.fpdc.com
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to