But again, the bottom line is that no, there are no requirements for sprinklers in a B occupancy.
They only get installed if you have sub-occupancies that require them, or the construction/area limitations require them, or the owner just wants them., etc. - but no requirements based strictly on the B occupancy classification. Mark A. Sornsin, PE | Fire Protection Engineer Ulteig Engineers, Inc. |Fargo, ND Direct: 701. 280.8591 | www.ulteig.com -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Todd Williams Sent: Wednesday, July 21, 2010 12:57 PM To: [email protected] Subject: IBC omission? I was looking for the section in IBC where they describe the maximum square footage where sprinklers are not required in a Group B occupancy. I could find reference to all of the other occupancy groups, but not B. Am I missing something? Todd G. Williams, PE Fire Protection Design/Consulting Stonington, CT 860.535.2080 www.fpdc.com _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)