But again, the bottom line is that no, there are no requirements for sprinklers 
in a B occupancy.

They only get installed if you have sub-occupancies that require them, or the 
construction/area limitations require them, or the owner just wants them., etc. 
- but no requirements based strictly on the B occupancy classification.

Mark A. Sornsin, PE | Fire Protection Engineer
Ulteig Engineers, Inc. |Fargo, ND
Direct:    701. 280.8591 | www.ulteig.com

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Todd Williams
Sent: Wednesday, July 21, 2010 12:57 PM
To: [email protected]
Subject: IBC omission?

I was looking for the section in IBC where they describe the maximum
square footage where sprinklers are not required in a Group B
occupancy. I could find reference to all of the other occupancy
groups, but not B. Am I missing something?

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com