I think Todd was referring to the ch 9 stuff.  Where you go after height and 
area tables tell you you don't need sprinklers but then ch 9 over rules that 
with a one size fits all based on use.  As in all R's required in ch 9 but not 
in ch 5 as an example.

If you think there was an error check the previous version.  Top-o-me head I 
don't recall B's.

Chris Cahill
Sent from my Verizon Wireless BlackBerry

-----Original Message-----
From: [email protected]
Sender: [email protected]
Date: Wed, 21 Jul 2010 14:23:54 
To: <[email protected]>
Reply-To: [email protected]
Subject: Re: IBC omission?

Yes. Sprinklers are required whenever the floor area exceeds the permitted 
allowable areas for a non-sprinklered building based upon the occupancy 
and the type of construction shown in Table 503.

Matt
Matthew Drewello, P.E. l FLUOR l Senior Design Engineer - Fire Protection 
l [email protected] l O +864.517.1814 l www.fluor.com




Todd Williams <[email protected]>
Sent by:  [email protected]
07/21/2010 02:18 PM
Please respond to sprinklerforum

To
[email protected]
cc

Subject
Re: IBC omission?








So I can have an office building with Type III construction at 28,500 
sqft and sprinklers are not required?



At 02:07 PM 7/21/2010, you wrote:
>Table 503 indicates the allowable height and building area based upon the
>type of construction for all use groups.
>
>Matt Drewello
>
>Matthew Drewello, P.E. l FLUOR l Senior Design Engineer - Fire Protection
>l [email protected] l O +864.517.1814 l www.fluor.com
>
>
>
>
>Todd Williams <[email protected]>
>Sent by:  [email protected]
>07/21/2010 01:57 PM
>Please respond to sprinklerforum
>
>To
>[email protected]
>cc
>
>Subject
>IBC omission?
>
>
>
>
>
>
>
>
>I was looking for the section in IBC where they describe the maximum
>square footage where sprinklers are not required in a Group B
>occupancy. I could find reference to all of the other occupancy
>groups, but not B. Am I missing something?
>
>Todd G. Williams, PE
>Fire Protection Design/Consulting
>Stonington, CT
>860.535.2080
>www.fpdc.com
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>------------------------------------------------------------
>The information transmitted is intended only for the person
>or entity to which it is addressed and may contain
>proprietary, business-confidential and/or privileged material.
>If you are not the intended recipient of this message you are
>hereby notified that any use, review, retransmission, dissemination,
>distribution, reproduction or any action taken in reliance upon
>this message is prohibited. If you received this in error, please
>contact the sender and delete the material from any computer.
>
>Any views expressed in this message are those of the individual
>sender and may not necessarily reflect the views of the company.
>------------------------------------------------------------
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

------------------------------------------------------------
The information transmitted is intended only for the person 
or entity to which it is addressed and may contain 
proprietary, business-confidential and/or privileged material.  
If you are not the intended recipient of this message you are 
hereby notified that any use, review, retransmission, dissemination, 
distribution, reproduction or any action taken in reliance upon 
this message is prohibited. If you received this in error, please 
contact the sender and delete the material from any computer.  

Any views expressed in this message are those of the individual 
sender and may not necessarily reflect the views of the company.  
------------------------------------------------------------
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to