When was it built? Does it meet the pipe schedule for then? Has it
changed use? Is there a local ordinance requiring upgrade for this
reason?

On Wed, Aug 11, 2010 at 9:13 AM, Todd Williams <[email protected]> wrote:
> I think I have this one, but could use a little more ammo. I walked through
> an old mill building this morning with an old OH pipe schedule system. (They
> want to convert from wet to dry). In the building, they have some 8 ft
> storage of a Group A plastics in cardboard cartons and well as 2 piles of
> idle pallets to 8 ft. The owner is claiming that the pipe schedule is
> grandfathered and the system does not need to meet the hydraulic criteria. I
> disagree and am basing most of my argument on the water supply requirements
> in 11.2.2 (NFPA 13, 2002 edition). Any other thoughts?
>
> Todd G. Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> 860.535.2080
> www.fpdc.com
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA

253.680.7346

Member:
AFSA, SFPE, ASCET, NFPA, NFSA, AFAA, ASEE, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis
Bacon, essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to