Again, I don't know why it would need to even comply with chapter 22
unless there is something in the applicable building code with any
legal amendments or in a local ordinance that would drive an upgrade
to current code. When I worked for a building department in California
we had if the occupancy changed or if the new work exceeded 25% of the
assessed value of the building for drivers. Other than that only NEW
work needed to meet the current code and then was modified by language
such as Forest cites about new work to old pipe schedule systems
needing to maintain the pipe schedule. Whatever your current 13 is it
is the standard for INSTALLATION of sprinkler systems, not the
revamping of existing systems. That is still governed by version of 13
under which the system was installed unless some other piece of
legislation contravenes or the existing condition is a danger to
public health or safety.

On Wed, Aug 11, 2010 at 12:54 PM, Forest Wilson <[email protected]> wrote:
> Roland is correct.
> NFPA does not state a 30% increase requirement.
> NFPA 13-11.2.3.2.5 requires a 30% increase for hydraulically calculated
> systems.
> However, 13-11.2.2.3 clearly states that "Additions or modifications to
> existing pipe schedule systems sized according to the pipe schedules"..shall
> be permitted.
> So, provided that the system piping complied with Chapter 22,this system
> could be converted from wet to dry using the pipe schedule system. It could
> be considered a modification not requiring hydraulic calcs with the
> increase.
>
> Forest Wilson
> Cherokee Fire
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of John O'Connor
> Sent: Wednesday, August 11, 2010 12:34 PM
> To: [email protected]; [email protected]
> Subject: RE: pipe schedule and storage
>
> And if the system is converted to dry can the existing pipe schedule afford
> the 30% area increase while flowing water thru two pieces of 1" at the end
> of all lines.  I doubt it.
> John O'Connor
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Brad
> Sent: Wednesday, August 11, 2010 11:26 AM
> To: [email protected]
> Subject: RE: pipe schedule and storage
>
> And hopefully it was installed long enough ago that sloping the pipe to
> drain was required on wet systems too
>
> -----Original Message-----
> From: [email protected] [mailto:[email protected]]
> Sent: Wednesday, August 11, 2010 11:21 AM
> To: [email protected]
> Subject: RE: pipe schedule and storage
>
> Typically if you're not touching the old system it can stay in place as-is.
> BUT if they want to modify it and try to change from wet to dry (good luck
> with that) then it's game over and it has to meet current codes.  The whole
> idea of grandfathering in non-compliant systems is a misnomer.
>
> Plus the big thing, how can you prove the system will function when changing
> from wet to dry without calculating it?
>
> Besides, when did the owner become a code and fire protection expert?  You
> just gotta love it.
>
> Craig L. Prahl, CET
> Fire Protection Specialist
> Mechanical Department
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> Spartanburg, SC  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> [email protected]
> http://www.ch2m.com
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Todd Williams
> Sent: Wednesday, August 11, 2010 12:14 PM
> To: [email protected]
> Subject: pipe schedule and storage
>
> I think I have this one, but could use a little more ammo. I walked
> through an old mill building this morning with an old OH pipe
> schedule system. (They want to convert from wet to dry). In the
> building, they have some 8 ft storage of a Group A plastics in
> cardboard cartons and well as 2 piles of idle pallets to 8 ft. The
> owner is claiming that the pipe schedule is grandfathered and the
> system does not need to meet the hydraulic criteria. I disagree and
> am basing most of my argument on the water supply requirements in
> 11.2.2 (NFPA 13, 2002 edition). Any other thoughts?
>
> Todd G. Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> 860.535.2080
> www.fpdc.com
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> No virus found in this incoming message.
> Checked by AVG - www.avg.com
> Version: 9.0.851 / Virus Database: 271.1.1/3064 - Release Date: 08/11/10
> 01:34:00
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA

253.680.7346

Member:
AFSA, SFPE, ASCET, NFPA, NFSA, AFAA, ASEE, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis
Bacon, essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to