Not entirely as Matthew said. It satisfies those applications where the standard prescribes that the hanger shall be of a type that resists upward movement only. Restraint (as described in 13) is a lesser form of lateral bracing and is to be installed at the specified intervals and ends of lines. And within 2' of a hanger that resists upward movement if I recall correctly (don't have 13 with me - riding shotgun with my 15-year old daughter at the moment).
Sent from my Verizon Wireless BlackBerry -----Original Message----- From: "Brian Harris" <[email protected]> Sender: <[email protected]> Date: Fri, 13 Aug 2010 06:47:29 To: <[email protected]> Reply-To: <[email protected]>Subject: Seismic Question Is a Surge Restraint (tolco #25) considered and End-Of-Line restraint per 9.3.6.3 (2007) ? Thanks! Brian Harris Design Engineer First Defense Fire Protection 11957 Ramah Church Road Huntersville NC 28078 [email protected] www.firstdefensefire.com <outbind://80/www.firstdefensefire.com> Ph: 704.948.3506 Fax: 704.948.3507 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) __________ Information from ESET NOD32 Antivirus, version of virus signature database 5364 (20100813)__________ The message was checked by ESET NOD32 Antivirus. http://www.eset.com _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)