I can't shed any light on the banner situations, but I am interested to
know what forumites normally consider for minimum gap between pipes on a
pipe rack exceeding 48" before they have to be considered a solid
obstruction.

Thanks,



James L (Jim) Roberts, PE/SET | FLUOR | Principal Fire Protection Engineer
– Central Engineering | [email protected] | IODC 20.5149 | O
+1.864.281.5149 | www.fluor.com





















From:       <[email protected]>
To:         <[email protected]>
Date:       10/04/2010 02:25 PM
Subject:    RE: multiple obstructions that total more than 48"
Sent by:    [email protected]



What kind of occupancy?   If these banners could come loose and fall would
it cause an egress issue for occupants trying to exit the area in an
emergency?

Essentially it sounds like these banners are creating a sub-level ceiling
below the sprinklers.  I believe in one of the previous discussions it was
mentioned about these types of items being suspended with some type of
fusible link so that they could drop out of the way of the sprinkler
discharge in a fire event.

Other issue is if they would not drop out of the way would they hold water
from a sprinkler to the point where the banner could either dump a large
amount of water on person below or fill to the point it could create an
issue with the structure's ability to support the weight?

What will 18" below the heads accomplish?

Suggestion: Put the banners on the wall.

Craig L. Prahl, CET
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com

-----Original Message-----
From: [email protected] [
mailto:[email protected]] On Behalf Of Ed Kramer
Sent: Monday, October 04, 2010 12:56 PM
To: [email protected]
Subject: multiple obstructions that total more than 48"

I recall this has been discussed, but not recently.



Is there guidance anywhere as to how much gap needs to be between
obstructions (each individual obstruction being no more than 48" wide) so
that sprinklers are not needed beneath them?



More specifically, I have a project where the architect would like to
install banners beneath the ceiling and does not want sprinklers beneath
the
banners.  I'm fairly confident he's  willing to lower the banners so
they're
at least 18" below the sprink deflectors.  He's also willing to make them
narrower (48" max wide). But he would like to place them as close together
as possible (without needing sprinks below them).



Anybody aware of any guidelines for this?



Ed Kramer

Littleton, CO

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
------------------------------------------------------------
The information transmitted is intended only for the person 
or entity to which it is addressed and may contain 
proprietary, business-confidential and/or privileged material.  
If you are not the intended recipient of this message you are 
hereby notified that any use, review, retransmission, dissemination, 
distribution, reproduction or any action taken in reliance upon 
this message is prohibited. If you received this in error, please 
contact the sender and delete the material from any computer.  

Any views expressed in this message are those of the individual 
sender and may not necessarily reflect the views of the company.  
------------------------------------------------------------
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to