I have done outdoor systems in pipe racks etc... at refineries along the Texas 
coast (hurricanes). The electrical devices had to be EP. The valves were cast 
steel epoxy lined but that was probably because of the water supply.

At the copper mine the specialty materials were already purchased. We furnished 
the pipe and did the install. There shouldn't be a problem if the electrical 
equipment has the proper NEMA rating.


Ron Fletcher
Aero Automatic
Phoenix, AZ

   

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Tuesday, October 19, 2010 6:50 AM
To: [email protected]
Subject: RE: Valve house requirement?

When you're in an area subject to hurricanes and you're protecting flammable 
liquid operations and storage, is it still ok to just let all the equipment sit 
out in the yard?

Ron, when you ordered equipment, did you order anything special for the outdoor 
application or just off the shelf items?

Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Fletcher, Ron
Sent: Tuesday, October 19, 2010 9:47 AM
To: [email protected]
Subject: RE: Valve house requirement?

I hope there isn't there is a standard that requires an enclosure. We
recently installed some systems at a copper mine with the AFFF tanks,
risers and other stuff outside. It is pretty easy to build a rack from
Unistrut and plywood to mount panels etc... One drawback might be the
shelf life of the AFFF concentrate but that can be monitored with
regular testing.

Ron Fletcher
Aero Automatic
Phoenix, AZ

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Tuesday, October 19, 2010 5:26 AM
To: [email protected]
Subject: Valve house requirement?

I have a situation where the "powers that be" want to just locate the
fire risers, foam tanks, control panels and all assorted trim and
accessories for two FP systems outside, exposed to the elements.  The
environment is a chemical plant in the SE.  Freezing is not an issue and
it's on private property not accessible to the public.  The one hazard
is a multi-level process structure w/ multiple deluge systems, the other
is fuel storage tanks with the foam protection.

I've given some verbiage from NFPA 13 concerning protection of equipment
but since someone who did the initial write-up forgot the houses, the
owner believes they are not needed.

Any specific code requirements?  Their idea is to order "weather proof"
equipment.  I guess they're going to hang the control panels by helium
balloons.

Craig L. Prahl

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to