Explain that 2007 is nothing but a big TIA for 2002, maybe that will switch
on the light bulb. 
Ken from the "other guys" explained it that way and it seemed to have
clarity- until the explanation fell on CMS's ears ni Blatimore and they
explained the DOH doesn't (in fact, can't) enforce a TIA to the 1999 #13 for
any health care facility in the US, no matter what the applicable building
code references for applicable edition of #13. So you need to design to 1999
#13 AND the applicable edition, if there is mixed AHJs DOH and Local/State.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Cliff
Whitfield
Sent: Tuesday, November 02, 2010 9:24 AM
To: [email protected]
Subject: RE: Mechanical closet obstruction

Todd,

I understand that you are using 2002 but I still believe a credible argument
exists in presenting the info from 2007.  The heads that are approved for
this condition are no different than the heads that you have installed.

Besides the section I already gave you (6.8.1.5.3.1) there is another that
is applicable - the 'shadow' rule - 6.7.7.1.5.7 - it sounds like what you
have meets this also.  In addition, if your mech room does not have a door
but merely an access panel the head is not even required unless it is a
gas-fired unit. (6.9.6)  All of these are from the 2007.  I don't have the
2002 handy.

Hope something helps with this situation!

Cliff
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Todd Williams
Sent: Tuesday, November 02, 2010 7:05 AM
To: [email protected]
Subject: RE: Mechanical closet obstruction

Probably to justify his job.

It is a 13R building under 2002. He didn't allow the exception because the
closet ceiling is greater than 5 ft (Actual 8ft). Still negotiating.


At 07:54 AM 11/2/2010, you wrote:
>Interesting how a design issue has now turned into an unreasonable AHJ
issue
>with demands for citations and suggestions for sprinkler locations.  
>Looks like big $ to reconfigure all these mechanical spaces to be able 
>to add sprinklers per their listings and avoid obstructions.  Why is 
>the AHJ under the gun to justify and negotiate at this point?
>
>Bill Brooks
>
>William N. Brooks, P.E.
>Brooks Fire Protection Engineering Inc.
>372 Wilett Drive
>Severna Park, MD 21146-1904
>410-544-3620
>410-544-3032 FAX
>412-400-6528 Cell
>
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of 
>[email protected]
>Sent: Tuesday, November 02, 2010 7:13 AM
>To: [email protected]
>Subject: RE: Mechanical closet obstruction
>
>So ask this AHJ where he would like you to place this non-code 
>compliant sprinkler in this space.I still think your best bet is to 
>place it in the corner,that way you cover the most floor space (1/2 of 
>2.222----REALLY???)and get enough water bouncing around this spce till 
>it finds the fire. :) And BTW,be sure to keep the head a minimum of 4" 
>off the wall ..... oh yea,you only HAVE 4".
>
>Lamar Vaughn
>
>
>On Mon, Nov 1, 2010 at 5:46 PM, Todd Williams wrote:
>
> > I agree. This was a "what do I do?" call from a client this afternoon.
> > He was going to try to meet with the AHJ, but he was the one who had 
> > written it up as being obstructed. Someone at the Convention asked 
> > me where I find these people. Directly or indirectly, they find me.
> >
> >
> > At 05:39 PM 11/1/2010, you wrote:
> >> It's kind of ridiculous that you have to even have a discussion 
> >> about this.  What's the AHJ want you to do?
> >>
> >> Craig L. Prahl, CET
> >> Fire Protection Specialist
> >> Mechanical Department
> >> CH2MHILL
> >> Lockwood Greene
> >> 1500 International Drive
> >> Spartanburg, SC  29304-0491
> >> Direct - 864.599.4102
> >> Fax - 864.599.8439
> >> [email protected]
> >> http://www.ch2m.com
> >>
> >>
> >> -----Original Message-----
> >> From: [email protected]
> >> [mailto:[email protected]] On Behalf Of Todd 
> >> Williams
> >> Sent: Monday, November 01, 2010 5:27 PM
> >> To: [email protected]
> >> Subject: RE: Mechanical closet obstruction
> >>
> >> The 16x16 duct runs vertically off the top of the unit. there is no 
> >> bottom of duct
> >>
> >>
> >>
> >> At 05:11 PM 11/1/2010, you wrote:
> >>> Blow up the HVAC unit?, just ;)
> >>>
> >>> Locate the head with deflector at bottom of the 16" deep 
> >>> obstruction. Show the section where head can be located up to 22" 
> >>> for obstructed construction.
> >>>
> >>> Tony
> >>>
> >>> -----Original Message-----
> >>> From: [email protected]
> >>> [mailto:[email protected]] On Behalf Of 
> >>> Todd Williams
> >>> Sent: November 1, 2010 3:01 PM
> >>> To: [email protected]
> >>> Subject: RE: Mechanical closet obstruction
> >>>
> >>> Existing condition. Not going to happen
> >>>
> >>>
> >>> At 04:43 PM 11/1/2010, you wrote:
> >>>> It may be hard for him to shove the HVAC unit against the wall.
> >>>> With
> >>>> the minimal space allowed in this closet he still needs room to 
> >>>> make duct connections, electrical connections, drain connections 
> >>>> etc.
> >>>> But
> >>>> hey you could ask.
> >>>>
> >>>> Craig L. Prahl, CET
> >>>> Fire Protection Specialist
> >>>> Mechanical Department
> >>>> CH2MHILL
> >>>> Lockwood Greene
> >>>> 1500 International Drive
> >>>> Spartanburg, SC  29304-0491
> >>>> Direct - 864.599.4102
> >>>> Fax - 864.599.8439
> >>>> [email protected]
> >>>> http://www.ch2m.com
> >>>>
> >>>>
> >>>> -----Original Message-----
> >>>> From: [email protected]
> >>>> [mailto:[email protected]] On Behalf Of 
> >>>> [email protected]
> >>>> Sent: Monday, November 01, 2010 4:25 PM
> >>>> To: [email protected]
> >>>> Subject: RE: Mechanical closet obstruction
> >>>>
> >>>> Todd,
> >>>> This is just a thought.Get the HVAC contractor to shift the unit 
> >>>> into the corner,then place the sprinkler in the opposite,leaving 
> >>>> 8"
> >>>> clear on
> >>>> 2 sides.You can maintain the 4" min. off the wall and cover ALL 
> >>>> the clear space in the room.Right?
> >>>>
> >>>> Lamar Vaughn
> >>>>
> >>>>
> >>>> On Mon, Nov 1, 2010 at 2:53 PM, Todd Williams wrote:
> >>>>
> >>>>> This is under the 2002 code and they have the 5 ft ceiling 
> >>>>> height restriction. I believe this is an 8 ft ceiling.
> >>>>>
> >>>>>
> >>>>>
> >>>>> At 02:28 PM 11/1/2010, you wrote:
> >>>>>> Todd,
> >>>>>>
> >>>>>> If this is residential, 6.8.1.5.3.1 specifically addresses this 
> >>>>>> concern.
> >>>>>> 2007 ed.
> >>>>>>
> >>>>>> Cliff
> >>>>>> -----Original Message-----
> >>>>>> From: [email protected]
> >>>>>> [mailto:[email protected]] On Behalf Of 
> >>>>>> Todd Williams
> >>>>>> Sent: Monday, November 01, 2010 1:22 PM
> >>>>>> To: [email protected]
> >>>>>> Subject: Mechanical closet obstruction
> >>>>>>
> >>>>>> I know this was referenced in another post, but I can't find it 
> >>>>>> so I'm starting a new thread.
> >>>>>>
> >>>>>> A 2' x 2' mechanical closet. The unit is mounted on the floor 
> >>>>>> and a 16" x 16" plenum comes off the top and runs up through 
> >>>>>> the ceiling at roughly the center of the room (approximately 4" 
> >>>>>> clearance on each side). One sidewall sprinkler is installed 
> >>>>>> near the ceiling and the AHJ questions the head being 
> >>>>>> obstructed. Outside of installing 4 sprinklers in the closet, 
> >>>>>> any good way to address this? The State Building Code 
> >>>>>> specifically excludes the application of
> >>> common sense.
> >>>>>> Thoughts?
> >>>>>>
> >>>>>> Todd G. Williams, PE
> >>>>>> Fire Protection Design/Consulting Stonington, CT
> >>>>>> 860.535.2080
> >>>>>> www.fpdc.com
> >>>>>>
> >>>>>> _______________________________________________
> >>>>>> Sprinklerforum mailing list
> >>>>>> [email protected] 
> >>>>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerfor
> >>>>>> um
> >>>>>>
> >>>>>> For Technical Assistance, send an email to:
> >>>>>> [email protected]
> >>>>>>
> >>>>>> To Unsubscribe, send an email
> >>>>>> to:[email protected]
> >>>>>> (Put the word unsubscribe in the subject field)
> >>>>>>
> >>>>>> _______________________________________________
> >>>>>> Sprinklerforum mailing list
> >>>>>> [email protected] 
> >>>>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerfor
> >>>>>> um
> >>>>>>
> >>>>>> For Technical Assistance, send an email to:
> >>>>>> [email protected]
> >>>>>>
> >>>>>> To Unsubscribe, send an email
> >>>>>> to:[email protected]
> >>>>>> (Put the word unsubscribe in the subject field)
> >>>>>
> >>>>> Todd G. Williams, PE
> >>>>> Fire Protection Design/Consulting Stonington, CT
> >>>>> 860.535.2080
> >>>>> www.fpdc.com
> >>>>>
> >>>>> _______________________________________________
> >>>>> Sprinklerforum mailing list
> >>>>> [email protected] 
> >>>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforu
> >>>>> m
> >>>>>
> >>>>> For Technical Assistance, send an email to:
> >>>>> [email protected]
> >>>>>
> >>>>> To Unsubscribe, send an email
> >>>>> to:[email protected]
> >>>>> (Put the word unsubscribe in the subject field)
> >>>> _______________________________________________
> >>>> Sprinklerforum mailing list
> >>>> [email protected]
> >>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>>>
> >>>> For Technical Assistance, send an email to:
> >>>> [email protected]
> >>>>
> >>>> To Unsubscribe, send an email
> >>>> to:[email protected]
> >>>> (Put the word unsubscribe in the subject field) 
> >>>> _______________________________________________
> >>>> Sprinklerforum mailing list
> >>>> [email protected]
> >>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>>>
> >>>> For Technical Assistance, send an email to:
> >>>> [email protected]
> >>>>
> >>>> To Unsubscribe, send an email
> >>>> to:[email protected]
> >>>> (Put the word unsubscribe in the subject field)
> >>>
> >>> Todd G. Williams, PE
> >>> Fire Protection Design/Consulting
> >>> Stonington, CT
> >>> 860.535.2080
> >>> www.fpdc.com
> >>>
> >>> _______________________________________________
> >>> Sprinklerforum mailing list
> >>> [email protected]
> >>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>>
> >>> For Technical Assistance, send an email to:
> >>> [email protected]
> >>>
> >>> To Unsubscribe, send an email
> >>> to:[email protected]
> >>> (Put the word unsubscribe in the subject field)
> >>>
> >>> _______________________________________________
> >>> Sprinklerforum mailing list
> >>> [email protected]
> >>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>>
> >>> For Technical Assistance, send an email to:
> >>> [email protected]
> >>>
> >>> To Unsubscribe, send an email
> >>> to:[email protected]
> >>> (Put the word unsubscribe in the subject field)
> >>
> >> Todd G. Williams, PE
> >> Fire Protection Design/Consulting
> >> Stonington, CT
> >> 860.535.2080
> >> www.fpdc.com
> >>
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> [email protected]
> >> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>
> >> For Technical Assistance, send an email to: 
> >> [email protected]
> >>
> >> To Unsubscribe, send an email
> >> to:[email protected]
> >> (Put the word unsubscribe in the subject field) 
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> [email protected]
> >> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>
> >> For Technical Assistance, send an email to: 
> >> [email protected]
> >>
> >> To Unsubscribe, send an email
> >> to:[email protected]
> >> (Put the word unsubscribe in the subject field)
> >
> > Todd G. Williams, PE
> > Fire Protection Design/Consulting
> > Stonington, CT
> > 860.535.2080
> > www.fpdc.com
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > For Technical Assistance, send an email to: 
> > [email protected]
> >
> > To Unsubscribe, send an email
> > to:[email protected]
> > (Put the word unsubscribe in the subject field)
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email 
>to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email 
>to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to