Interesting how a design issue has now turned into an unreasonable AHJ issue
with demands for citations and suggestions for sprinkler locations.  Looks
like big $ to reconfigure all these mechanical spaces to be able to add
sprinklers per their listings and avoid obstructions.  Why is the AHJ under
the gun to justify and negotiate at this point?

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Tuesday, November 02, 2010 7:13 AM
To: [email protected]
Subject: RE: Mechanical closet obstruction

So ask this AHJ where he would like you to place this non-code compliant 
sprinkler in this space.I still think your best bet is to place it in 
the corner,that way you cover the most floor space (1/2 of 
2.222----REALLY???)and get enough water bouncing around this spce till 
it finds the fire. :)
And BTW,be sure to keep the head a minimum of 4" off the wall ..... oh 
yea,you only HAVE 4".

Lamar Vaughn


On Mon, Nov 1, 2010 at 5:46 PM, Todd Williams wrote:

> I agree. This was a "what do I do?" call from a client this afternoon. 
> He was going to try to meet with the AHJ, but he was the one who had 
> written it up as being obstructed. Someone at the Convention asked me 
> where I find these people. Directly or indirectly, they find me.
>
>
> At 05:39 PM 11/1/2010, you wrote:
>> It's kind of ridiculous that you have to even have a discussion about 
>> this.  What's the AHJ want you to do?
>>
>> Craig L. Prahl, CET
>> Fire Protection Specialist
>> Mechanical Department
>> CH2MHILL
>> Lockwood Greene
>> 1500 International Drive
>> Spartanburg, SC  29304-0491
>> Direct - 864.599.4102
>> Fax - 864.599.8439
>> [email protected]
>> http://www.ch2m.com
>>
>>
>> -----Original Message-----
>> From: [email protected] 
>> [mailto:[email protected]] On Behalf Of Todd 
>> Williams
>> Sent: Monday, November 01, 2010 5:27 PM
>> To: [email protected]
>> Subject: RE: Mechanical closet obstruction
>>
>> The 16x16 duct runs vertically off the top of the unit. there is no
>> bottom of duct
>>
>>
>>
>> At 05:11 PM 11/1/2010, you wrote:
>>> Blow up the HVAC unit?, just ;)
>>>
>>> Locate the head with deflector at bottom of the 16" deep 
>>> obstruction. Show
>>> the section where head can be located up to 22" for obstructed 
>>> construction.
>>>
>>> Tony
>>>
>>> -----Original Message-----
>>> From: [email protected]
>>> [mailto:[email protected]] On Behalf Of Todd 
>>> Williams
>>> Sent: November 1, 2010 3:01 PM
>>> To: [email protected]
>>> Subject: RE: Mechanical closet obstruction
>>>
>>> Existing condition. Not going to happen
>>>
>>>
>>> At 04:43 PM 11/1/2010, you wrote:
>>>> It may be hard for him to shove the HVAC unit against the wall. 
>>>> With
>>>> the minimal space allowed in this closet he still needs room to 
>>>> make
>>>> duct connections, electrical connections, drain connections etc. 
>>>> But
>>>> hey you could ask.
>>>>
>>>> Craig L. Prahl, CET
>>>> Fire Protection Specialist
>>>> Mechanical Department
>>>> CH2MHILL
>>>> Lockwood Greene
>>>> 1500 International Drive
>>>> Spartanburg, SC  29304-0491
>>>> Direct - 864.599.4102
>>>> Fax - 864.599.8439
>>>> [email protected]
>>>> http://www.ch2m.com
>>>>
>>>>
>>>> -----Original Message-----
>>>> From: [email protected]
>>>> [mailto:[email protected]] On Behalf Of
>>>> [email protected]
>>>> Sent: Monday, November 01, 2010 4:25 PM
>>>> To: [email protected]
>>>> Subject: RE: Mechanical closet obstruction
>>>>
>>>> Todd,
>>>> This is just a thought.Get the HVAC contractor to shift the unit 
>>>> into
>>>> the corner,then place the sprinkler in the opposite,leaving 8" 
>>>> clear on
>>>> 2 sides.You can maintain the 4" min. off the wall and cover ALL the
>>>> clear space in the room.Right?
>>>>
>>>> Lamar Vaughn
>>>>
>>>>
>>>> On Mon, Nov 1, 2010 at 2:53 PM, Todd Williams wrote:
>>>>
>>>>> This is under the 2002 code and they have the 5 ft ceiling height
>>>>> restriction. I believe this is an 8 ft ceiling.
>>>>>
>>>>>
>>>>>
>>>>> At 02:28 PM 11/1/2010, you wrote:
>>>>>> Todd,
>>>>>>
>>>>>> If this is residential, 6.8.1.5.3.1 specifically addresses this
>>>>>> concern.
>>>>>> 2007 ed.
>>>>>>
>>>>>> Cliff
>>>>>> -----Original Message-----
>>>>>> From: [email protected]
>>>>>> [mailto:[email protected]] On Behalf Of 
>>>>>> Todd
>>>>>> Williams
>>>>>> Sent: Monday, November 01, 2010 1:22 PM
>>>>>> To: [email protected]
>>>>>> Subject: Mechanical closet obstruction
>>>>>>
>>>>>> I know this was referenced in another post, but I can't find it 
>>>>>> so
>>>>>> I'm starting a new thread.
>>>>>>
>>>>>> A 2' x 2' mechanical closet. The unit is mounted on the floor and 
>>>>>> a
>>>>>> 16" x 16" plenum comes off the top and runs up through the 
>>>>>> ceiling
>>>>>> at roughly the center of the room (approximately 4" clearance on
>>>>>> each side). One sidewall sprinkler is installed near the ceiling
>>>>>> and the AHJ questions the head being obstructed. Outside of
>>>>>> installing 4 sprinklers in the closet, any good way to address
>>>>>> this? The State Building Code specifically excludes the 
>>>>>> application of
>>> common sense.
>>>>>> Thoughts?
>>>>>>
>>>>>> Todd G. Williams, PE
>>>>>> Fire Protection Design/Consulting
>>>>>> Stonington, CT
>>>>>> 860.535.2080
>>>>>> www.fpdc.com
>>>>>>
>>>>>> _______________________________________________
>>>>>> Sprinklerforum mailing list
>>>>>> [email protected]
>>>>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>>>>
>>>>>> For Technical Assistance, send an email to:
>>>>>> [email protected]
>>>>>>
>>>>>> To Unsubscribe, send an email
>>>>>> to:[email protected]
>>>>>> (Put the word unsubscribe in the subject field)
>>>>>>
>>>>>> _______________________________________________
>>>>>> Sprinklerforum mailing list
>>>>>> [email protected]
>>>>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>>>>
>>>>>> For Technical Assistance, send an email to:
>>>>>> [email protected]
>>>>>>
>>>>>> To Unsubscribe, send an email
>>>>>> to:[email protected]
>>>>>> (Put the word unsubscribe in the subject field)
>>>>>
>>>>> Todd G. Williams, PE
>>>>> Fire Protection Design/Consulting
>>>>> Stonington, CT
>>>>> 860.535.2080
>>>>> www.fpdc.com
>>>>>
>>>>> _______________________________________________
>>>>> Sprinklerforum mailing list
>>>>> [email protected]
>>>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>>>
>>>>> For Technical Assistance, send an email to:
>>>>> [email protected]
>>>>>
>>>>> To Unsubscribe, send an email
>>>>> to:[email protected]
>>>>> (Put the word unsubscribe in the subject field)
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>>
>>>> For Technical Assistance, send an email to: 
>>>> [email protected]
>>>>
>>>> To Unsubscribe, send an email
>>>> to:[email protected]
>>>> (Put the word unsubscribe in the subject field)
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>>
>>>> For Technical Assistance, send an email to: 
>>>> [email protected]
>>>>
>>>> To Unsubscribe, send an email
>>>> to:[email protected]
>>>> (Put the word unsubscribe in the subject field)
>>>
>>> Todd G. Williams, PE
>>> Fire Protection Design/Consulting
>>> Stonington, CT
>>> 860.535.2080
>>> www.fpdc.com
>>>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>
>>> For Technical Assistance, send an email to: 
>>> [email protected]
>>>
>>> To Unsubscribe, send an email 
>>> to:[email protected]
>>> (Put the word unsubscribe in the subject field)
>>>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>
>>> For Technical Assistance, send an email to: 
>>> [email protected]
>>>
>>> To Unsubscribe, send an email 
>>> to:[email protected]
>>> (Put the word unsubscribe in the subject field)
>>
>> Todd G. Williams, PE
>> Fire Protection Design/Consulting
>> Stonington, CT
>> 860.535.2080
>> www.fpdc.com
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email 
>> to:[email protected]
>> (Put the word unsubscribe in the subject field)
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email 
>> to:[email protected]
>> (Put the word unsubscribe in the subject field)
>
> Todd G. Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> 860.535.2080
> www.fpdc.com
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]
> (Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to