Yup, it was printed in 2004, unfortunately that's the only "white paper" that I 
see regarding Residential and it's posted on their website.   Think a bit of 
updating might be in order!  :)
Carrol


________________________________
From: Roland Huggins <[email protected]>
To: [email protected]
Sent: Tue, November 2, 2010 9:24:00 AM
Subject: Re: Residential "Room Design Method"?

well it didn't occur in 02 so it wouldn't be in OLD Tyco data.  As others have 
pointed out, the explicit reference in 13:11.3 is all the fire power one needs.

Roland

On Nov 2, 2010, at 9:10 AM, Carrol Glimstad wrote:

> Makes perfect sense to me!  But, BUT what do I do when I look to NFPA to give 
>me
> some fire power to help with convincing my plan reviewer and "they" come back
> with the response that small rooms are NOT allowed to be considered in
> residential applications?  I guess I'm assuming that when the sprinkler head's
> manufacturer's cut sheet states " a minimum discharge of 0.1 GPM/sq. ft. over
> the "design area" comprised of the four most hydraulically demanding 
sprinklers
> for actual coverage areas protected by the four sprinklers.", that "actual"
> means ACTUAL.  Yes, my head is 10 feet off of two walls, but my flow table on 
>my
> LFII cut sheet tells me that I can and that I'm gonna hit that back wall as 
>long
> as I have the flow and pressure to back it up.  But my actual coverage area is
> NOT 400 sq. ft.!  Not even close.
> 
> It doesn't help my situation either when in the Tyco white paper on 
"Residental
> Sprinklers Used in NFPA 13, 2002 Applications", the author makes NO reference 
>at
> all to 8.6.2.1.2.  He only cites the S x L rule for determining coverage 
areas.
> (big sigh...)
> 
> Carrol Glimstad
> Sierra Fire Design
> 
> 
> 
> 
>


      
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to