Sounds like the ahj grew up in pipe schedule days where bigger always fed 
smaller.  Same guys that call an outside bell a water motor gong, even if 
electric.
 
An example that is explicit in 13:  adding a return bend by replacing a 1/2" 
upright with a nipple and 1x1/2x1 tee.  Without looking it up, I believe you 
can go as much as 6" on the 1/2 nip.

Dave 

David A. de Vries, P.E., CSP 
Firetech Engineering Incorporated 




--- On Thu, 11/11/10, Todd Williams <[email protected]> wrote:


From: Todd Williams <[email protected]>
Subject: reduce then increase pipe sizes
To: [email protected]
Date: Thursday, November 11, 2010, 7:50 AM


I am working on an existing system where we have to tie in a new 2-1/2" main 
into an existing 3". Since they do not make a 3x2-1/2 mechanical tee, that 
option is out. My proposal is to utilize an existing plugged 2" outlet, install 
a 2 x 0-6 TxG nipple and then increase to 2-1/2". It works hydraulically with 
18+ psi left over (reducing the 2-1/2" main not an option hydraulically).

I don't see anything in the Code that states that it is not allowed. However, 
the AHJ says it isn't. Before I argue the point, am I missing something?

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to