Per NFPA you can't weld pipe in the field.

On Fri, Nov 12, 2010 at 8:56 AM, [email protected] <[email protected]> wrote:
>
> Can you have a reducing tee welded up?  Or again, are the clearances too 
> tight?
>
>
>>Cc      :
>>Subject : RE: Re: reduce then increase pipe sizes
>>
>  >That would be great is we had clear access to the
> pipe to do that. This is a 100+ year old mill
> (and 100+ y.o. system) and there are lots of
> other things in the vicinity of the main. We
> would have to go a lot further away to be able to do that.
>
>
> At 09:36 AM 11/11/2010, you wrote:
>> From a. Fitters asspect. I would just cut the
>> 3" main , roll groove it in place and install a
>> 3" grooved tee then reduce the bull outlet Tom
>> berry Precision fire protection
>> Service/inspections [email protected]. Sent
>
>>
> Subject:
>> reduce then increase pipe sizes I am working on
>> an existing system where we have to tie in a
>> new 2-1/2" main into an existing 3". Since they
>> do not make a 3x2-1/2 mechanical tee, that
>> option is out. My proposal is to utilize an
>> existing plugged 2" outlet, install a 2 x 0-6
>> TxG nipple and then increase to 2-1/2". It
>> works hydraulically with 18+ psi left over
>> (reducing the 2-1/2" > _______________________________________________
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
AFSA, SFPE, ASCET, NFPA, NFSA, AFAA, ASEE, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis
Bacon, essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to