Can you have a reducing tee welded up?  Or again, are the clearances too tight?


>Cc      : 
>Subject : RE: Re: reduce then increase pipe sizes
>
 >That would be great is we had clear access to the 
pipe to do that. This is a 100+ year old mill 
(and 100+ y.o. system) and there are lots of 
other things in the vicinity of the main. We 
would have to go a lot further away to be able to do that.


At 09:36 AM 11/11/2010, you wrote:
> From a. Fitters asspect. I would just cut the 
> 3" main , roll groove it in place and install a 
> 3" grooved tee then reduce the bull outlet Tom 
> berry Precision fire protection 
> Service/inspections [email protected]. Sent 

> 
Subject: 
> reduce then increase pipe sizes I am working on 
> an existing system where we have to tie in a 
> new 2-1/2" main into an existing 3". Since they 
> do not make a 3x2-1/2 mechanical tee, that 
> option is out. My proposal is to utilize an 
> existing plugged 2" outlet, install a 2 x 0-6 
> TxG nipple and then increase to 2-1/2". It 
> works hydraulically with 18+ psi left over 
> (reducing the 2-1/2" > _______________________________________________ 


_______________________________________________