In think only on high rise and that may be just local. I don't have a
IBC handy and I think the high rise section may be where such a
requirement might be found.

On Thu, Dec 9, 2010 at 2:52 PM, Ed Kramer <[email protected]> wrote:
> Apologies if this has been discussed previously.  Is anyone aware of a code
> requirement for a "main" flow switch?  This would only occur in a building
> with multiple systems (such as 1 wet and 1 dry, or 3 wet, etc).  The "main"
> flow switch would be located upstream of the individual system risers and
> would be in addition to the flow switches/pressure switches on the wet/dry
> systems.  I've seen a number of projects where they are called for, but am
> curious if it's a code requirement or not.
>
>
>
> Ed Kramer
>
> Littleton, CO
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
AFSA, SFPE, ASCET, NFPA, NFSA, AFAA, ASEE, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis
Bacon, essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to