Consider the FF's if you do one.  Try to set the retard the shortest so it's 
not on the panel when the FF's arrive.  If they see the zone actually causing 
the alarm it will get the water mitigation started faster.

Chris
-----Original Message-----
From: David de Vries <[email protected]>
Sender: [email protected]
Date: Thu, 9 Dec 2010 17:06:27 
To: <[email protected]>
Reply-To: [email protected]
Subject: Re: "main" flow switch

Ed:
 
Unless a high-rise, 13 only requires a single flow switch for an entire 
building.  I am not aware of a "main" flow switch as a code requirement, but as 
an engineer I have often spec'd one, typically in the pump room downstream of 
the pump, where there are multiple systems, or floors, supplied through a feed 
main.  Flow switches have been known to fail and having redundancy provides a 
level of comfort, especially if there is a long run of feed main.  I do know 
that the pump controller is wired for supervision, but if the building is 
monitored by an alarm service, that signal comes in as a supervisory, not an 
alarm that rolls the trucks. 

Dave 

David A. de Vries, P.E., CSP 
Firetech Engineering Incorporated 



--- On Thu, 12/9/10, Ed Kramer <[email protected]> wrote:


From: Ed Kramer <[email protected]>
Subject: "main" flow switch
To: [email protected]
Date: Thursday, December 9, 2010, 4:52 PM


Apologies if this has been discussed previously.  Is anyone aware of a code
requirement for a "main" flow switch?  This would only occur in a building
with multiple systems (such as 1 wet and 1 dry, or 3 wet, etc).  The "main"
flow switch would be located upstream of the individual system risers and
would be in addition to the flow switches/pressure switches on the wet/dry
systems.  I've seen a number of projects where they are called for, but am
curious if it's a code requirement or not.



Ed Kramer

Littleton, CO 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to