Ed:
 
Unless a high-rise, 13 only requires a single flow switch for an entire 
building.  I am not aware of a "main" flow switch as a code requirement, but as 
an engineer I have often spec'd one, typically in the pump room downstream of 
the pump, where there are multiple systems, or floors, supplied through a feed 
main.  Flow switches have been known to fail and having redundancy provides a 
level of comfort, especially if there is a long run of feed main.  I do know 
that the pump controller is wired for supervision, but if the building is 
monitored by an alarm service, that signal comes in as a supervisory, not an 
alarm that rolls the trucks. 

Dave 

David A. de Vries, P.E., CSP 
Firetech Engineering Incorporated 



--- On Thu, 12/9/10, Ed Kramer <[email protected]> wrote:


From: Ed Kramer <[email protected]>
Subject: "main" flow switch
To: [email protected]
Date: Thursday, December 9, 2010, 4:52 PM


Apologies if this has been discussed previously.  Is anyone aware of a code
requirement for a "main" flow switch?  This would only occur in a building
with multiple systems (such as 1 wet and 1 dry, or 3 wet, etc).  The "main"
flow switch would be located upstream of the individual system risers and
would be in addition to the flow switches/pressure switches on the wet/dry
systems.  I've seen a number of projects where they are called for, but am
curious if it's a code requirement or not.



Ed Kramer

Littleton, CO 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to