Exactly - I should have used the term "looking over" instead of "reviewing" in the initial message. Yes the drawing shows 20 sprinklers enclosed in a nice shaded box. However the calculation entry data shows each sprinkler at 95 sq ft. So based on a first glance at the shaded area and the graph things looked OK but they weren't.
Now I'm "reviewing". Bill Brooks William N. Brooks, P.E. Brooks Fire Protection Engineering Inc. 372 Wilett Drive Severna Park, MD 21146-1904 410-544-3620 410-544-3032 FAX 412-400-6528 Cell -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Roland Huggins Sent: Friday, December 17, 2010 11:00 AM To: [email protected] Subject: Re: 0.58 over 2000 I would start with checking the actually floor area (and likely finding it too small) since many still simply count the number of sprinklers. It doesn't help that the Sprinkler Handbook babbles for several pages on counting sprinklers (at least it did the last time I checked that section). What a waste of space in a good book! Roland On Dec 16, 2010, at 1:23 PM, Bill Brooks wrote: > Reviewing a hydraulic calc for a 0.58 over 2000 gridded warehouse > system. > All seemed OK until I reached the BOR flow of 1143 gpm. From this I > assume > the selected design area isn't correct since there's no way a 0.58 > over 2000 > system should flow less than 1160 gpm. I've never heard of hydraulic > imbalance that results in lower overall flow. Am I crazy or is > there a new > version of sprinkler hydraulics out there? > > Bill Brooks > > William N. Brooks, P.E. > Brooks Fire Protection Engineering Inc. > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)