Not crazy, just someone who knows what he's looking at. Kudos! As others have stated, there's a whole number of reasons this could happen. You can either reject the submittals outright (and make the designer figure out where he/she went wrong), or spend the time to figure it out yourself. Either way, it's nice to see a plan reviewer pick-up on something like that.
Ed Kramer Littleton, CO > Reviewing a hydraulic calc for a 0.58 over 2000 gridded warehouse > system. > All seemed OK until I reached the BOR flow of 1143 gpm. From this I > assume > the selected design area isn't correct since there's no way a 0.58 over > 2000 > system should flow less than 1160 gpm. I've never heard of hydraulic > imbalance that results in lower overall flow. Am I crazy or is there a > new > version of sprinkler hydraulics out there? > > Bill Brooks > > William N. Brooks, P.E. > Brooks Fire Protection Engineering Inc. > _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)