On 12/16/2010 4:42 PM, Todd Williams wrote:
Reject!

Check the actual sprinkler spacing, K factor and calculate the minimum end head pressure. See if it matches the minimum in the calc. Also check if all the heads in the remote area are flowing.


At 04:23 PM 12/16/2010, you wrote:
Reviewing a hydraulic calc for a 0.58 over 2000 gridded warehouse system. All seemed OK until I reached the BOR flow of 1143 gpm. From this I assume the selected design area isn't correct since there's no way a 0.58 over 2000
system should flow less than 1160 gpm.  I've never heard of hydraulic
imbalance that results in lower overall flow. Am I crazy or is there a new
version of sprinkler hydraulics out there?

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

--
Greg C. McGahan Living Water Fire Protection, LLC. 1160 McKenzie Road Cantonment, FL 32533 850-937-1850 Fax 850-937-1852
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to