By the letter, yes the AHJ is correct. The section states "Static or
Flowing..." No, I have never had the issue come up.

Would a small relief valve set @ 99 psi be ok?

 
R/
Matt

Ps
do not forget the hanger closest to the sprinkler shall be of a type to
prevent upward movement...
 

Matthew J. Willis, CET
Automatic Fire Sprinklers
Norred Fire Systems L.L.C.
318-387-1134 Voice
318-816-1087 Mobile
318-387-1163 Facsimile
[email protected]

> >-----Original Message-----
> >From: [email protected] [mailto:sprinklerforum-
> >[email protected]] On Behalf Of Sam Kassab
> >Sent: Thursday, January 20, 2011 12:47 PM
> >To: [email protected]
> >Subject: Hangers and pressure surges
> >
> >NFPA requires hangers to be installed on armovers over 12" when operating
> >pressure is over 100 PSI.  What if normal street pressure is below 100
> >PSI
> >and pressure surges cause a build-up of 100 PSI or more on the system
> >side
> >of the check valve?  The AHJ's argument is that the system will have over
> >100 PSI when the system first operates, albeit for a brief moment.  Is
> >the
> >AHJ correct in his interpretation of this requirement?  Has anyone ever
> >come
> >across this question?
> >
> >
> >
> >Thanks in advance.
> >
> >
> >
> >Sam Kassab
> >
> >TridenT FIRE PROTECTION, INC.
> >
> >13631 Pawnee Rd. , Suite A-1
> >
> >Apple Valley, CA 92308
> >
> >Tel :   (760) 961-7222
> >
> >Fax :  (866) 501-5942
> >
> >Cell:  (805) 801-4676
> >
> >Lic.  C-16 935502
> >
> > <mailto:[email protected]> [email protected]
> >
> >
> >
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> >For Technical Assistance, send an email to: [email protected]
> >
> >To Unsubscribe, send an email to:[email protected]
> >(Put the word unsubscribe in the subject field)
> >
> >No virus found in this incoming message.
> >Checked by AVG - www.avg.com
> >Version: 9.0.872 / Virus Database: 271.1.1/3375 - Release Date: 01/19/11
> >13:34:00

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to