The issue is most problematic when the head first pops.  So I think the AHJ has 
a point.  Oh and 9.2.3.4.4.1 seems to actually support the AHJ legally where it 
clearly says static or flowing.

Now if your real static without surge is below 100 you have the option of 
controlling surges instead or changing hangers as I would interpret.

Chris 
-----Original Message-----
From: "Sam Kassab" <[email protected]>
Sender: [email protected]
Date: Thu, 20 Jan 2011 10:46:49 
To: <[email protected]>
Reply-To: [email protected]
Subject: Hangers and pressure surges

NFPA requires hangers to be installed on armovers over 12" when operating
pressure is over 100 PSI.  What if normal street pressure is below 100 PSI
and pressure surges cause a build-up of 100 PSI or more on the system side
of the check valve?  The AHJ's argument is that the system will have over
100 PSI when the system first operates, albeit for a brief moment.  Is the
AHJ correct in his interpretation of this requirement?  Has anyone ever come
across this question?

 

Thanks in advance.

 

Sam Kassab

TridenT FIRE PROTECTION, INC.

13631 Pawnee Rd. , Suite A-1

Apple Valley, CA 92308

Tel :   (760) 961-7222

Fax :  (866) 501-5942

Cell:  (805) 801-4676

Lic.  C-16 935502

 <mailto:[email protected]> [email protected]

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to