What is an Addsco Annular Wedge (for 50)

George Church
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE       570-837-6335 fax
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Jim Davidson
Sent: Friday, February 11, 2011 3:56 PM
To: [email protected]
Subject: RE: misaligned flanges

Tom,

Some time ago one of my clients seem to have had a similar problem and he 
purchased a gasket shim kit from a pipe fabrication house which specialized in 
welded flange pipe segments. From client the firm had gaskets that were slipped 
in between standard flat flange gaskets to take up angular flange face 
misalignment. I cannot remember the name of the firm and my client contact has 
pasted on to a better place. That is what happens when you gain enough 
experance.

Have a fire safe day.

Regards

Jim Davidson 
 
Davidson Associates
Fire Protection * Medical Gas * Code Consulting
302-994-9500   Fax:302-234-1781


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Tom Duross
Sent: Friday, February 11, 2011 3:16 PM
To: [email protected]
Subject: RE: misaligned flanges

Thanks for the responses, I thought the thread was dead (no pun).  The system 
side is 1/8" lower than the street side so something has to spring or the riser 
shortened and it's 8" s40 threaded into flanges, 40 years old.
Pipe stands are what I plan to use, 3/4" rod inside 3/4" pipe with  a 10"
riser clamp around the wafer check and brackets for 30 degree braces to the 
wall.  They were never lined up right I found when it dropped and it's right 
below a 4' duct where the valve-check-valve assembly is, so no way to hang from 
structure.  There also is no o-ring (as one might expect), just flat faces to 
mate to the OS&Y flanges.  I was thinking of some RTV sealant as a high tack to 
hold the gaskets and maybe help seal but I'm still going to have misalignment 
which is my original quandary.  Use really long wrenches on the 3/4" rods?  
Double gaskets?


More hangers will not work. The pipe develops "memory" and springs to that 
spot. Pipe stands can help, but often there is other stuff in the way. Short of 
chasing the leak around the flange, gaskets are the only control. 
Are crush gaskets still available?

Matt

Sent from my phone thingy.


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to