Thanks Thom-- that was Chris' 10 MW fire when he was AHJ. He ruled no
sprinklers at that height, and stands behind the decision still, and FWIW, I
am standing beside him. 

-----Original Message-----
From: Thom [mailto:[email protected]] 
Sent: Monday, February 21, 2011 11:35 AM
To: [email protected]
Subject: RE: 'seeing' heat release rate

Brad:

I think if you look at the archives, we were discussing sports arena at one
time, and Roland brought up a 10Kw fire on the floor about I think 120'
below the fire sprinkler system as what the fire had grown too or was set at
to activate the ceiling protection of this light haz. Occ. I think the
discussion was more about delay in operation, and the allowance in IBC for
no system over the floor area of the arena, but I'm sure if you work search
Kw or kw or kilowatt, you'll get a lot of the reference info.

Not an answer, just some thoughts.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Brad
Casterline
Sent: Sunday, February 20, 2011 12:40 PM
To: [email protected]
Subject: 'seeing' heat release rate

A while back I was going to post the question 'does anybody know the numbers
that go with the text in 13- low, moderate and high heat release rate?' I am
an Eng. Tech., and so only responsible for applying 13, not writing it, but
being from the 'Show Me State', I would have had to 'see' the numbers
anyway, and so decided to take a shot at them on my own. I wanted to share
what I came up with. I like being right, but I love being corrected if Ii am
not, so..., please, anyone. For a Burning Unit, I see a big dry Christmas
tree, either standing on the floor, or stuffed in to a one cubic foot box
weighing 33 pounds. I call them both 'tree'. How hot is a Light Hazard fire?
If you throw a tree on it, the tree would be gone in 16 seconds. There are
114 trees per 1500 square feet~~ 13 square feet per tree. The next time I
max out an EC head in LH, I will see 30 trees under it, so I will make sure
to get enough water to it! For Heat of Combustion I used 22,500 kilo-joules
per kilo-gram (fire power). For the amount of water required to keep the
power of the fire in check, for LH, I used .1/1500 for 30 minutes, with Heat
of Vaporization for water of 2257 kilo-joules per kilo-gram. How hot is an
Ordinary Hazard Group 2 fire? If you threw a tree on it, the tree would be
gone in 8 seconds. There are 228 trees per 1500 square feet~~6.5 square feet
per tree. The numbers for OH1 fall right between LH and OH2. Based on all
this, I now think Low Heat Release Rate means a 2.1 Megawatt fire, and a
Moderate Heat Release Rate means a 4.2 Megawatt fire. If I am in the
ballpark, I am 2/3 of the way to knowing the number for High Heat Release
Rate.

 

ps- if you are aggravated bcoz this post stuffed your phone at Sunday brunch
I owe u an apology: i'm sorry ur so touchy :-)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to