Experimenters have shown that the Heat of Combustion for a wide range of
combustibles is directly proportional to the amount of O2 consumed= 13,100
Kj/Kg (12,428 BTU/lb).

If so, 1 gallon of water per square foot will handle 7 pounds of fuel per
square foot.

A Christmas tree lot would only be LH if business had been good and this was
Christmas Eve.

Now the Burning Unit is a box weighing 19 pounds~ a 'case'*~~ playing like
beer is an average combustible.

A study of 3 hospitals in 1942 came up with an average fuel load of ~6
pounds per square foot- (an 8-pack).

How hot is a Light Hazard Fire? I have no idea.

 

*When I dropped out of college a 'case' was 24 beers. According to the
fraternity I TAPPA KEG, a 'case' is now 30 beers. I still use 24.

 

Ps- At the risk of spinning this until ridiculously twisted, how satisfying
would it be to look for Max Deflector Distance and find-

For Unobstructed Construction= Not TOO far down.

For Obstructed Construction= 1.83 times Unobstructed.

?

 

 

 

 

 

  

 

 

 