Brad:
 
I don't want to open a bucket of worms discussion-wise, but obviously, what's 
burning in a "typical" light or ordinary hazard compartment could be very 
different within a "uniform" hazard group occupancy.   If my desk and the 
mountain of papers scattered across it were to be involved in a fire, the 
overall release would be WAY lower than if the sofa in our lobby was involved.  
 All light hazard, but our lobby is a much higher potential energy load.
 
SL

________________________________

From: [email protected] on behalf of Brad Casterline
Sent: Sun 2/27/2011 10:22 AM
To: [email protected]
Subject: re- 'seeing' heat release rate



Experimenters have shown that the Heat of Combustion for a wide range of
combustibles is directly proportional to the amount of O2 consumed= 13,100
Kj/Kg (12,428 BTU/lb).

If so, 1 gallon of water per square foot will handle 7 pounds of fuel per
square foot.

A Christmas tree lot would only be LH if business had been good and this was
Christmas Eve.

Now the Burning Unit is a box weighing 19 pounds~ a 'case'*~~ playing like
beer is an average combustible.

A study of 3 hospitals in 1942 came up with an average fuel load of ~6
pounds per square foot- (an 8-pack).

How hot is a Light Hazard Fire? I have no idea.



*When I dropped out of college a 'case' was 24 beers. According to the
fraternity I TAPPA KEG, a 'case' is now 30 beers. I still use 24.



Ps- At the risk of spinning this until ridiculously twisted, how satisfying
would it be to look for Max Deflector Distance and find-

For Unobstructed Construction= Not TOO far down.

For Obstructed Construction= 1.83 times Unobstructed.

?











 







_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to