You can do it either way. BUT, you have to ensure that all scenarios are proven hydraulically...the most remote area is not necessarily the most demanding area. So, you may have to provide more than one calc. It depends.
Duane Johnson, PE Program Manager Division of the Fire Marshal (Support Contractor) Office of Research Services National Institutes of Health 301-496-0487 "Protecting Science - One Sprinkler at a Time" -----Original Message----- From: [email protected] [mailto:[email protected]] Sent: Tuesday, February 22, 2011 1:36 AM To: [email protected] Subject: As = L x S Hi I understand that I need to use the maximum AS (sprinkler coverage) to run the hydraulic calculations. Is This AS should be taken from only the sprinklers in the remote area, or should be for the entire system??? Regards _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)