You can do it either way.  BUT, you have to ensure that all scenarios are 
proven hydraulically...the most remote area is not necessarily the most 
demanding area.  So, you may have to provide more than one calc.  It depends. 

Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Support Contractor)
Office of Research Services 
National Institutes of Health 
301-496-0487

"Protecting Science - One Sprinkler at a Time"


-----Original Message-----
From: [email protected] [mailto:[email protected]] 
Sent: Tuesday, February 22, 2011 1:36 AM
To: [email protected]
Subject: As = L x S

Hi
I understand that I need to use the maximum AS (sprinkler coverage) to run
the hydraulic calculations. Is This AS should be taken from only the
sprinklers in the remote area, or should be for the entire system???