If you are referring to the area of coverage of the individual sprinkler you 
should use the actual area the sprinkler is covering not the maximum allowable. 
 If you have sprinklers spaced where they cover only 90 square feet due to 
obstructions or other construction issues, use that value regardless whether or 
not your maximum allowable spacing may have been 130 square feet. 

You are only calculating the sprinklers in the hydraulically remote area unless 
you are calculating a deluge system.

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Tuesday, February 22, 2011 1:36 AM
To: [email protected]
Subject: As = L x S

Hi
I understand that I need to use the maximum AS (sprinkler coverage) to run
the hydraulic calculations. Is This AS should be taken from only the
sprinklers in the remote area, or should be for the entire system???
Regards


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to