If you are referring to the area of coverage of the individual sprinkler you should use the actual area the sprinkler is covering not the maximum allowable. If you have sprinklers spaced where they cover only 90 square feet due to obstructions or other construction issues, use that value regardless whether or not your maximum allowable spacing may have been 130 square feet.
You are only calculating the sprinklers in the hydraulically remote area unless you are calculating a deluge system. Craig L. Prahl, CET Fire Protection CH2MHILL Lockwood Greene 1500 International Drive Spartanburg, SCĀ 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 CH2MHILL Extension 74102 [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of [email protected] Sent: Tuesday, February 22, 2011 1:36 AM To: [email protected] Subject: As = L x S Hi I understand that I need to use the maximum AS (sprinkler coverage) to run the hydraulic calculations. Is This AS should be taken from only the sprinklers in the remote area, or should be for the entire system??? Regards _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)