Shall we all make a pact right here and follow Duane and quit using
the term "remote area" and instead shift to "most hydraulically
demanding area(s)" or just "most demanding area(s)?" The term remote
confuses new techs as well as many seasoned ones (techs in this sense
also includes engineers that are equally confused) and is a
mythological memory of a distant past when most sprinklered buildings
were warehouses and factories, primarily large (not to be confused
with "Big") boxes, where the terms most demanding and remote were
typically synonymous. One obvious area out in the south forty is
rarely the case any longer. Let's toss the "term" remote along with
the some of the more idiotic explanations I've heard here for the 52K
ft^2 limitation, the FD lost looking for the FDC (that they really
use) reasons for a WMG, etc. As B & J used to say, "Thank you for your
support."

On Tue, Feb 22, 2011 at 5:40 AM,  <[email protected]> wrote:
> If you are referring to the area of coverage of the individual sprinkler you 
> should use the actual area the sprinkler is covering not the maximum 
> allowable.  If you have sprinklers spaced where they cover only 90 square 
> feet due to obstructions or other construction issues, use that value 
> regardless whether or not your maximum allowable spacing may have been 130 
> square feet.
>
> You are only calculating the sprinklers in the hydraulically remote area 
> unless you are calculating a deluge system.
>
> Craig L. Prahl, CET
> Fire Protection
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> Spartanburg, SC  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> CH2MHILL Extension  74102
> [email protected]
>
>
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of 
> [email protected]
> Sent: Tuesday, February 22, 2011 1:36 AM
> To: [email protected]
> Subject: As = L x S
>
> Hi
> I understand that I need to use the maximum AS (sprinkler coverage) to run
> the hydraulic calculations. Is This AS should be taken from only the
> sprinklers in the remote area, or should be for the entire system???
> Regards
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis
Bacon, essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to