I've seen the hose allowance taken at the base of the riser and seen it taken 
at the Source node at the connection point of the riser to the underground 
service main.  It really depends on your layout, whether you have internal hose 
connections or not.



Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Tuesday, February 22, 2011 1:36 AM
To: [email protected]
Subject: Hose allowance

Hi.
I remember that the hose allowance is added in the hydraulic calculation in
the node where the remote area ends over the cross main.
Some people tell me that should be at the base of riser. We just purchase
AutoSpring and the software do this addition on the pump room
What is the way this should be?
Regards!