I have 3 gridded ESFR systems with three small hose stations in the
facility. I need to apply a total of 250gpm hose allowance to calc's. I am
supplying the small hose stations from adjacent systems. The first system
does not feed any hose stations, the middle system feeds two (one under each
adjacent system) and the third system feeds one (under the middle system).
When applying inside hose to the calc's, do I flow two of the hose stations
at 50gpm and apply to all three sets of calc's or would I flow 250 outside
for the first system; 150 outside for the middle with both hose stations
supplied off of this system flowing 50 each and then 200 outside for the
third with 50 gpm flowing out of the one supplied from this system? By the
way pump only - no tank.

 