I personally design for the fire to start anywhere. You have to look at the
system, not the device...

R/
Matt

 

 

Matthew J. Willis
Automatic Fire Sprinklers
Norred Fire Systems L.L.C.
318-387-1134 Voice
318-816-1087 Mobile
318-387-1163 Facsimile
[email protected]

> >-----Original Message-----
> >From: [email protected] [mailto:sprinklerforum-
> >[email protected]] On Behalf Of Brad Casterline
> >Sent: Thursday, March 10, 2011 10:31 AM
> >To: [email protected]
> >Subject: RE: partial walls in mech rooms
> >
> >From 24 to 42 square feet of floor (the floor is where we design for the
> >fire starting)-- does this floor space require a thousand or two square
> >feet
> >of sprinklers?
> >
> >-----Original Message-----
> >From: Matthew J. Willis [mailto:[email protected]]
> >Sent: Thursday, March 10, 2011 10:17 AM
> >To: [email protected]
> >Subject: RE: partial walls in mech rooms
> >
> >?
> >
> >
> >
> >
> >
> >Matthew J. Willis
> >Automatic Fire Sprinklers
> >Norred Fire Systems L.L.C.
> >318-387-1134 Voice
> >318-816-1087 Mobile
> >318-387-1163 Facsimile
> >[email protected]
> >
> >> >-----Original Message-----
> >> >From: [email protected] [mailto:sprinklerforum-
> >> >[email protected]] On Behalf Of Brad Casterline
> >> >Sent: Thursday, March 10, 2011 10:10 AM
> >> >To: [email protected]
> >> >Subject: RE: partial walls in mech rooms
> >> >
> >> >I cannot get past the idea that we normally put water on floors, not
> >on
> >> >the
> >> >tops of ceilings!
> >> >
> >> >-----Original Message-----
> >> >From: Greg McGahan [mailto:[email protected]]
> >> >Sent: Thursday, March 10, 2011 10:00 AM
> >> >To: [email protected]
> >> >Subject: Re: partial walls in mech rooms
> >> >
> >> >It is not CLEAR, this section appears to refer to the "cloud"
> >situation
> >> >we
> >> >are often running into.
> >> >
> >> >I am not trying to get out of something here, I am trying to document
> >why
> >> >we
> >> >have to do it. We have used the 15' rule in the past, but again, that
> >is
> >> >truly intended for another situation, in my honest opinion. This
> >section
> >> >is
> >> >to avoid fusing heads in adjacent areas, not require additional
> >> >protection... as I read it.
> >> >
> >> >On Thu, Mar 10, 2011 at 9:47 AM, Morey, Mike <[email protected]> wrote:
> >> >
> >> >> On second reading, if you're saying the LH areas have a ceiling but
> >the
> >> >> mechanical rooms don't then 8.15.22 does apply, in which case the
> >> >higher
> >> >> area is the roof deck, which means you provide the protection for
> >the
> >> >> mechanical room at the deck and for 24' in any direction away from
> >the
> >> >> mechanical room over the ceiling of the LH space.
> >> >>
> >> >> -Mike Morey, SET
> >> >> Sprinkler Designer
> >> >> BMW Constructors, Inc.
> >> >> office: 317-651-0596
> >> >> mobile: 317-439-2695
> >> >>
> >> >> ________________________________
> >> >>
> >> >> From: [email protected] on behalf of Greg
> >> >McGahan
> >> >> Sent: Thu 3/10/2011 10:21 AM
> >> >> To: [email protected]
> >> >> Subject: partial walls in mech rooms
> >> >>
> >> >>
> >> >>
> >> >> We have an issue right now with a light hazard non-combustible
> >building
> >> >in
> >> >> which there are multiple small mechanical rooms -3' x 8' or 6' x 7'
> >in
> >> >> general size. The architect was vague so the GC is not putting in
> >> >ceilings
> >> >> nor is he running the walls up to the deck.
> >> >>
> >> >> I have been reading and rereading chapter 8 of 13 -2010 edition, and
> >I
> >> >> cannot conclusively determine what we are required to do in this
> >case.
> >> >The
> >> >> description in 8.15.22.1 is not exactly correct so I can't see
> >> >clearly...
> >> >>
> >> >> Does anybody have a cut and dry answer?
> >> >> Thanks,
> >> >> Greg
> >> >>
> >> >> --
> >> >> Greg McGahan
> >> >> Living Water Fire Protection, LLC
> >> >> 1160 McKenzie Road
> >> >> Cantonment, FL 32533
> >> >> 850-937-1850
> >> >> fax 850-937-1852
> >> >> _______________________________________________
> >> >> Sprinklerforum mailing list
> >> >> [email protected]
> >> >> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >> >>
> >> >> For Technical Assistance, send an email to:
> >[email protected]
> >> >>
> >> >> To Unsubscribe, send an email to:Sprinklerforum-
> >> >[email protected]
> >> >> (Put the word unsubscribe in the subject field)
> >> >>
> >> >>
> >> >> _______________________________________________
> >> >> Sprinklerforum mailing list
> >> >> [email protected]
> >> >> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >> >>
> >> >> For Technical Assistance, send an email to:
> >[email protected]
> >> >>
> >> >> To Unsubscribe, send an email to:Sprinklerforum-
> >> >[email protected]
> >> >> (Put the word unsubscribe in the subject field)
> >> >>
> >> >
> >> >
> >> >
> >> >--
> >> >Greg McGahan
> >> >Living Water Fire Protection, LLC
> >> >1160 McKenzie Road
> >> >Cantonment, FL 32533
> >> >850-937-1850
> >> >fax 850-937-1852
> >> >_______________________________________________
> >> >Sprinklerforum mailing list
> >> >[email protected]
> >> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >> >
> >> >For Technical Assistance, send an email to: [email protected]
> >> >
> >> >To Unsubscribe, send an email to:Sprinklerforum-
> >[email protected]
> >> >(Put the word unsubscribe in the subject field)
> >> >
> >> >_______________________________________________
> >> >Sprinklerforum mailing list
> >> >[email protected]
> >> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >> >
> >> >For Technical Assistance, send an email to: [email protected]
> >> >
> >> >To Unsubscribe, send an email to:Sprinklerforum-
> >[email protected]
> >> >(Put the word unsubscribe in the subject field)
> >> >No virus found in this incoming message.
> >> >Checked by AVG - www.avg.com
> >> >Version: 9.0.872 / Virus Database: 271.1.1/3493 - Release Date:
> >03/10/11
> >> >01:34:00
> >
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> >For Technical Assistance, send an email to: [email protected]
> >
> >To Unsubscribe, send an email to:[email protected]
> >(Put the word unsubscribe in the subject field)
> >
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> >For Technical Assistance, send an email to: [email protected]
> >
> >To Unsubscribe, send an email to:[email protected]
> >(Put the word unsubscribe in the subject field)
> >
> >No virus found in this incoming message.
> >Checked by AVG - www.avg.com
> >Version: 9.0.872 / Virus Database: 271.1.1/3493 - Release Date: 03/10/11
> >01:34:00

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to