Your original post said the largest space was 7'x 8' or 56 SF. You may want
to discuss the cost of fire sprinklers vs. the cost of a drop ceiling in
these spaces.


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Greg McGahan
Sent: Thursday, March 10, 2011 9:45 AM
To: [email protected]
Subject: Re: partial walls in mech rooms

Well, you have to go 24 feet which ends up being an area of approx, 55' x
54' that you are now required to put heads in. I Although the example in the
handbook refers to a warehouse/office space in which the clarification is
that protection must extend 24' over the offices and the area of greater
hazard is outside the 24' zone, I guess it is similar, but it is a stretch
in my opinion.

In this case, the greater hazard is surrounded by a lesser hazard on 4
sides, Therefore if 8.15.22.3 applies, we will end up protecting the entire
non-combustible interstitial space. Before I argue for this change order I
want to make sure this is the intent on the code.

Thanks,
Greg