I know that and you know that, but I am loading my guns to fight a very
difficult GC.I just needed chapter and verse.

Thanks for all of the input, but I still very much feel that this is a grey
area that can be argued wither way.
Greg

On Thu, Mar 10, 2011 at 1:03 PM, Thom <[email protected]> wrote:

>
> Your original post said the largest space was 7'x 8' or 56 SF. You may want
> to discuss the cost of fire sprinklers vs. the cost of a drop ceiling in
> these spaces.
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Greg
> McGahan
> Sent: Thursday, March 10, 2011 9:45 AM
> To: [email protected]
> Subject: Re: partial walls in mech rooms
>
> Well, you have to go 24 feet which ends up being an area of approx, 55' x
> 54' that you are now required to put heads in. I Although the example in
> the
> handbook refers to a warehouse/office space in which the clarification is
> that protection must extend 24' over the offices and the area of greater
> hazard is outside the 24' zone, I guess it is similar, but it is a stretch
> in my opinion.
>
> In this case, the greater hazard is surrounded by a lesser hazard on 4
> sides, Therefore if 8.15.22.3 applies, we will end up protecting the entire
> non-combustible interstitial space. Before I argue for this change order I
> want to make sure this is the intent on the code.
>
> Thanks,
> Greg
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Greg McGahan
Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
fax 850-937-1852
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to