I'm looking at some pre-designed fire sprinkler drawings showing extended 
coverage uprights in a concealed combustible space above a grid ceiling 
consisting of open web wood trusses (relatively no pitch) at 24" o/c. 

Looking at 8.4.3. (2007 ed) I don't think this is permissible mainly because of 
the "smooth, flat" criteria. Am I right? And does someone make an EC upright 
that can possibly be used in this scenario (besides the Tyco attic sprinklers).

Thanks,
 Ralph




      