So when can we ever apply this rule if we must satisfy both FM and
AHJ(nfpa 13)? 

Dewayne Martinez
Design Build Fire Protection
New Berlin, WI


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Tuesday, March 15, 2011 12:51 AM
To: [email protected]
Subject: RE: FM Guildelines / ESFR

It comes in that point at the end:
The additional sprinklers installed under the obstruction as recommended
above do not need to be added to the hydraulic design of the
ceiling-level sprinkler system.

Enviado desde mi WebMail de CEPI


----------------------------------------
From: "Ed Kramer" <[email protected]>
Sent: Monday, March 14, 2011 11:05 PM
To: [email protected], [email protected]
Subject: RE: FM Guildelines / ESFR 

Travis, FM Data sheet 2-0, section 2.2.3.5.1, last paragraph (page 56)
may be what you're looking for.

Ed Kramer
Littleton, CO

> 
> Is it my imagination, or did I read somewhere that you are not req'd 
> to include the 2 heads under an obstruction in ESFR calculations with 
> the revised FM criteria.  If I was not imagining, where would that be
found?
> 
> --
> Please feel free to call if you have any questions or comments.
> 
> Sincerely,
> 
> Travis Mack, SET
> MFP Design, LLC
> 2508 E Lodgepole Drive
> Gilbert, AZ 85298
> Office (480) 505-9271
> Fax (866) 430-6107
> 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to