Section 8.4 shows the application requirements by type of sprinkler.
That's where it says for residential and ESFR wet pipe only (unless
listed for dry). Since 8.4.3 on EC does not have such a statement,
there is no such restriction.
Roland
On Mar 24, 2011, at 6:10 AM, Matt Grise wrote:
Forum,
I am having a little brain glitch this morning: Can EC heads be used
on dry pipe systems?
Thanks,
Matt Grisé PE*, LEED AP
Sales Engineer
Alliance Fire Protection
130 w 9th Ave.
North Kansas City, MO 64116
*Licensed in KS & MO
913.888.0647 ph
913.888.0618 f
913.927.0222 cell
www. AFPsprink.com