I don't unless in Glycol systems. I only have 8 years experience compared to 
AHJs, and NICET IV posts on here. I speak from the field, I wish to obtain 
NICET 
in Inspections one day. Glycol systems spring leaks. When you have a wet, or 
dry 
system, you only need white dope, and tape. Dope and tape the threads from the 
300 side, dope only on the fitting, or shopside side. It doesn't matter if you 
use tape or dope first, but dope on the outside of threads helps you make up 
deeper in the threads. By dry, I include Pre Action systems. Note, when I run a 
main drain, I use dope only. I've never had a drain leak, and I've run drains 
coming from 220 psi static.



      