TYCO makes a wet EC SW that will throw 24'-0 for OH Group II
Trust me guys, I'm not in favor of this and don't even think they should be wet! I gotta bid as directed, that's why I want them to give the direction so it can be hashed out later through CO. Bobby Gillett Sr. Project Manager Key Fire Protection, Inc. (731) 424-0130 office (731) 424-9285 fax (731) 267-4853 cell <mailto:[email protected]> [email protected] _____ From: [email protected] [mailto:[email protected]] On Behalf Of Thom Sent: Monday, March 28, 2011 1:36 PM To: [email protected] Subject: RE: Extended Coverage Dry SW for STORAGE Based upon that requirement .3/2500 you are looking for a HSW listed for both extended coverage and EH1 listing! Good luck with that, the 22'-0" made OH unlikely but EHI---- 13, 2007 11.2.3.2.2.4 Extended coverage sprinklers shall be listed with and designed for the minimum flow corresponding to the density for the hazard as specified in Figure 11.2.3.1.1. -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Bobby Gillett Sent: Monday, March 28, 2011 12:03 PM To: [email protected] Subject: RE: Extended Coverage Dry SW for STORAGE Not at this point; they don't want a dry system and want wet SW's. They haven't said what the storage criteria is but said to protect it at .3/2500. Bobby Gillett Sr. Project Manager Key Fire Protection, Inc. (731) 424-0130 office (731) 424-9285 fax (731) 267-4853 cell <mailto:[email protected]> [email protected] _____ From: [email protected] [mailto:[email protected]] On Behalf Of [email protected] Sent: Monday, March 28, 2011 12:27 PM To: [email protected] Subject: RE: Extended Coverage Dry SW for STORAGE Bad idea. Guess they won't back up on their concept of SW's huh? Whether the head will transmit enough cold to cause a freezing condition inside depends on the climate. But I wouldn't put any money on it unless you were in S. Texas, Arizona, Fla or So. Cal. Just curious but what density did they call out for the storage area? Did they list what materials were being stored or just pick a "it felt good" Hazard category from NFPA 13? Craig L. Prahl, CET Fire Protection CH2MHILL Lockwood Greene 1500 International Drive Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 CH2MHILL Extension 74102 [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Bobby Gillett Sent: Monday, March 28, 2011 1:20 PM To: [email protected] Subject: RE: Extended Coverage Dry SW for STORAGE OK I sent the question to the Arch/Engineer and they said they want to use wet SW's and if only the head is outside and pipe is in an insulated wall it won't freeze(?!?!?!). So now I need to find an EC SW listed for storage that will throw 16' under one canopy and 22'-0 under the other. Of course I cannot find one; any know of any I might be overlooking? Thank you, Bobby Gillett Sr. Project Manager Key Fire Protection, Inc. (731) 424-0130 office (731) 424-9285 fax (731) 267-4853 cell <mailto:[email protected]> [email protected] _____ From: [email protected] [mailto:[email protected]] On Behalf Of [email protected] Sent: Monday, March 28, 2011 11:19 AM To: [email protected] Subject: RE: Extended Coverage Dry SW for STORAGE If it's in the spec you need to provide it. What's the problem? Seriously, if it's storage they should have considered a dry system based on the depth of the area. The walkway, not enough info. If it's just a convenience walkway and not part of a required egress path, constructed of non-combustible components, not designed to accommodate any storage and separated from the occupied part of a building by a non-combustible separation it PROBABLY won't require to be sprinklered but more info would have to be shared to render a more substantial yeah or nay. Craig L. Prahl, CET Fire Protection CH2MHILL Lockwood Greene 1500 International Drive Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 CH2MHILL Extension 74102 [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Bobby Gillett Sent: Saturday, March 26, 2011 1:58 PM To: [email protected] Subject: Exteneded Coverage Dry SW for STORAGE Anyone heard of one of these? Project we r bidding is asking for Dry sidewalls for exterior storage canopies - one is 22'-0 deep and the other is 16'-0. The best I could find was an EC Dry SW for OH that throws up to 20'-0. I believe they need a dry system for each one. While I am at it they have a "covered walkway" (as its labeled) 11'-6 deep attached to building - not requesting sprinklers but I feel they will have to it. What say ye? Thanks, Bobby Gillett Sr. Project Manager Key Fire Protection, Inc. (731) 424-0130 office (731) 424-9285 fax (731) 267-4853 cell <mailto:[email protected]> [email protected] _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _____ No virus found in this message. Checked by AVG - www.avg.com Version: 10.0.1204 / Virus Database: 1498/3535 - Release Date: 03/28/11 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _____ No virus found in this message. Checked by AVG - www.avg.com Version: 10.0.1204 / Virus Database: 1498/3535 - Release Date: 03/28/11 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _____ No virus found in this message. Checked by AVG - www.avg.com Version: 10.0.1204 / Virus Database: 1498/3535 - Release Date: 03/28/11 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)
