K8 heads could actually penalize his design in the OH-I area couldn't they?  7 
psi minimum end head dictates 14ish GPM out of a k5.6, even at 130 sq ft going 
to a K8 head would actually cause him to discharge more GPM than the density 
requires (at least using my not particularly well calibrated internal 
calculator), and GPM as we know is what creates friction loss.  In the LH area 
if he spaced the heads out near the limits a K8 will save him some pressure, 
but given his water supply that doesn't look to be his biggest concern.  The 
big question is how long the 1 1/4" run is in my mind, if it's short enough you 
can jump up at the connection, if it isn't then you don't have a lot of options 
unless maybe you can squeeze out some area reductions (QR/Ceiling height 
reductions if they haven't been considered) with careful code reading and head 
selection.
 
Mike Morey, SET
Sprinkler Designer
BMW Constructors, Inc.
O: 317.651.0596 | C: 317.439.2695
www.bmwc.com 
<https://owa.bmwc.com/exchweb/bin/redir.asp?URL=http://www.bmwc.com> 
 

________________________________

From: [email protected] on behalf of Ron Greenman
Sent: Mon 4/4/2011 12:49 PM
To: [email protected]
Subject: Re: Design solution needed



What K heads are you using. Bigger holes help more than bigger pipes
in good pressure/bad water situations. If you're using K5.6 see the
huge gain K8.0 will give you. And your moister recent post asked most
of the questions I asked just as that left and yours arrived.



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to