NFPA 291 Chapter 4 suggests that the flow test should produce a flow equal to the necessary flow for fire fighting operations or a 25% drop from static at the residual hydrant. It says right in the standard only one hydrant needs to be flowed on a weak supply to meet those conditions. Mike Morey, SET, CFPS Sprinkler Designer BMW Constructors, Inc. O: 317.651.0596 | C: 317.439.2695 www.bmwc.com
________________________________ From: [email protected] on behalf of Brian Harris Sent: Wed 4/6/2011 9:49 AM To: [email protected] Subject: Flow Test I swear I once read that a single hydrant flow test was acceptable, maybe in limited instances, but I can't seem to find anything on it. Any ideas? Brian Harris First Defense Fire Protection 11957 Ramah Church Road Huntersville, NC 28078 Phone: 704.948.3506 Fax: 704.948.3507 Nicet # 128476 ======= Email scanned by PC Tools - No viruses or spyware found. (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.17210) http://www.pctools.com/ ======= _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)